Multiple Feed Forward Control
AustralIan
Jan 2013
Leipzig, Germany
1,368
I have a conveyor full of product in an oven, I am trying to control the final temperature of the product using conveyor speed.
I have 4 product temperature sensors along the conveyor.
I want to use a PID loop on the final product sensor, with summed feed forward from the 3 upstream temperature sensors.
My tuning parameters will be:
PID: Autotune while ignoring the feedforward
FF Gain: Usually I would introduce a disturbance, let the PID controller compensate, and set the FF Gain to Change(d) / Change(Output). But now I have three FF's which are related, not sure whether to divide by 3 or similar.
FF Lead: lag time of controller
FF Lag: time to get from this product temperature to the final product temp
Main question is on the FF Gains, but other advice welcome.
This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
147
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
500
I have 9 field devices, three METSEPM5110 power meters and six ACE949-2 rs285 interface modules. I want to read this Modbus rtu data through rs485...
317
I'm trying to use DTM browser to make make modbus poll from RTAC. I'm able to get the points in first poll object. But not able to get anything in...
127
Hello, I encountered a problem with the kinetix 6500 drive, error code s22, loss of 3 phase voltage. After disassembling and replacing the thermal...