Need Help About Profibus Network
Feb 2004
HI THERE
IF I'M USING PROFIBUS NETWORK FOR SCADA AND IF I HAVE TO DECIDE BAUD RATE FOR COMMUNICATION. SO WHAT ARE THE POINT TO BE CONSIDERED WHILE CALCULATING NETWORK LOAD AND HOW BAND WIDTH IS CALCULATED
deshpande_anmol said:
HI THERE
The length of network and slowest device will determine maximum baud rate. The number of devices on a segment is limited to 32. A repeater is required with more devices. As more devices are added to the scan list the scan interval will get longer but, Profibus DP usually updates MUCH faster than the control loop or the ability to process the data.
Yes, it is usually faster, but you should at least check the bus update time if the number of nodes approaches 50 or so.
I just worked on a project that had 85 nodes, and the I/O updates took 18ms. My scan time was 9ms, so my process image tables were lagging behind my scan. This is usually not even important, but I had several inputs that were only on for 25ms (I had no control over this), and I would miss them once in a while when the 18ms update and 9ms scan were out of synch just right. S7 gives you a ballpark time for the update by going to the Hardware Configuration, clicking on the ProfiBus network, and then clicking Properties>Network Settings>Bus Parameters.
Hello, I have some basic questions to ask about Profibus. Tt will be a little long to explain all, but I prefer giving all details to help people...
2,728
Hiya, In the past I have worked with AB PLCs, Citect, DH+ but I have recently changed jobs and struggling with the changes. Sometimes dont know...
1,676
We have around 140 MOV connected on profibus-DP in a ring topology(typical distance is around 1.5 kms) . These MOV will be connected to Schneider...
3,856
WE JUST SHIPPED TWO 45-65% COMPLETE MACHINES TO CHINA. BOTH LINES HAVE S7-414 PLC'S, IL-70 TOUCHPANEL PC'S AND SIMOVERT MASTERDRIVES 6SE7035-1EKG0...
3,459
I have a system using a S7-318DP. I have purchased a Diagnostic Repeater and placed in the network to try and gain insight to problems we have...
2,040