Need some Profibus help
Marioplc
Aug 2013
France
Hello, I have some basic questions to ask about Profibus.
Tt will be a little long to explain all, but I prefer giving all details to help people understand my problem with the context.
I don't know Profibus very well but today I went to a factory because their automation specialist is on holiday. The reason given was: the CPU S7-400 lost its program by battery default and they needed someone to upload it....
However, when I looked it, the S7-412 had a flash memory card inserted (eventhough it still has a battery?), so I doubted it could have lost its program. I tried to connect with my pc in every possible way but I couldn't. The four first LEDs were full RED (INTF, EXTF, BUS1F, BUS2F), the MPI port (BUS1F) too so impossible to connect. I concluded it was damaged, opened it and confirmed it.
They also had a 24V power supply which was exposed to water and was flashing immediately when powered. It wasn't the dedicated power supply of the CPU, but a sitop powersupply used to supply the I/O and decentralized periphery.
Now here come the problem. The SITOP power supply was replaced by some 24V PS they had in stock. I changed the CPU with another one they had, slightly different. A CPU 412-2 too, but with another reference, and a firmware 5.3 instead of a firmware 3.
When I transfer the HW, it understands that it's not the exact same version, but accept it anyway, and the CPU turn into RUN mode.
However, the profibus is in default. And here is something that surprised me a lot:
Eventough on their Profibus network they have one cable from the cpu profibus connector going to a serial of Siemens and the other going to a first IM151, then a second IM151 and then a HMI, in their hardware configuration, they only have one IM151 (the second one in the topology) and nothing else on the profibus network.
It surprised me because I always thought all slaves must be configured in the master project. But here, no. How is that possible? They told me this program works and always worked witht hat configuration.
The IM151's have the top two led flashing red in the same time for some seconds, then the second one flashing red alone, and then the double flashing cycle begins again.
One other thing, they repaced the first IM151 this month(with added I/O) and told me they just unplugged Profibus connectors then plugged it exactly how it was when they installed the new IM151)
I am in the process of checking the quality of the connections in the profibus connectors, but what others things should I look after?
The HW configuration thing puzzles me. Could the SITOP damage the IM151s? The leds of most the I/O of IM151's are green.
The DP slaves must be present in the HW Config. The HMI does not have to be present.
Investigate the diagnostics buffer (all of it, not just the last entry !).
Also investigate the Hardware Diagnostics.
They tell me the program was working like that. You confirm it's impossible if the slaves aren't in the HW config?
The program in itself is hard to analyze (no commentary and symbols, just adresses)
As for the diagnostics buffer, it doesn't help. The message is always the same. And in "module state" of the IM, it says that it doesn't exist.
Hiya, In the past I have worked with AB PLCs, Citect, DH+ but I have recently changed jobs and struggling with the changes. Sometimes dont know...
1,676
We have around 140 MOV connected on profibus-DP in a ring topology(typical distance is around 1.5 kms) . These MOV will be connected to Schneider...
3,855
WE JUST SHIPPED TWO 45-65% COMPLETE MACHINES TO CHINA. BOTH LINES HAVE S7-414 PLC'S, IL-70 TOUCHPANEL PC'S AND SIMOVERT MASTERDRIVES 6SE7035-1EKG0...
3,457
I have a system using a S7-318DP. I have purchased a Diagnostic Repeater and placed in the network to try and gain insight to problems we have...
2,040
HI THERE IF I'M USING PROFIBUS NETWORK FOR SCADA AND IF I HAVE TO DECIDE BAUD RATE FOR COMMUNICATION. SO WHAT ARE THE POINT TO BE CONSIDERED...
5,084