New ML1200
Jezz
Dec 2002
Kendal
399
Hi All, I'm having an issue with a brand new Allen Bradley ML1200 I can't get connected to it ,I'm using a direct conection via an RS232 port (set up for DF1) I've checked the DF1 conection on a ML1100 I had spare and it's fine any ideas?
The settings I'm using are :
Baud rate 19200
Station number 00
Parity None
Error Checking CRC
Stop Bits 1
Protocol Ful Duplex
Its possible the port on your ML1200 is not configured for DF1 protocol, it could be DH485 or ASCII.
You can default the comm port to DF1 see PDF below for how to do this.
What happens when you click autoconfigure in RSLinx?
I've tried to default the com port but I can't get the DCOM LED to come on , if I do an auto-configure I just get Failed to find the baud and parity! Check all cables and switch settings!I know the cable is fine so it must be the com settings on the ML1200 but its a brand new one so I don't get why the coms would be difrent from default and why I can't get the DCOM LED to light
Hey all! Long time reader, first time poster! I have an EA9-T7CL and an MicroLogix 1200 connected via DF1. I'm all good and got everything mostly...
660
Hi every master,Recently i met a fault about 1762-L40BWA 1,When i get the PLC, The Fault light is lighting, I am not remember the fault message,I...
722
Hello everybody and master,I met a problem about ML1200.It is described as below: 1,When i got this PLC,The FAULT light is lighting, My computer...
1,118
I had planned to use PTO instructions to control a servo motor, single axis only. We have a ML1200 BWA model. According to the ML1200 manual...
3,499
I am using Modbus to read 36 registers from a ML1200. 2 of those registers are suppose to be L11 data and 2 of the registers are F8 data. Long...
1,404