Number of local expansion modules, max - AB
Ptolemies
Apr 2017
Manila
Hi everyone. In the manual of AB CompactLogix, it is stated there the number of local expansion modules, max. My question is, are the modules connected via Ethernet count as expansion modules? Or the number of modules connected via ethernet has another max limit?
Thanks!
It refers to local modules which includes I/O and comms and I believe it is based of off power consumption and backplane bus loading.
Also take note some compactlogix models require you to pay attention to distance from power supply and is why you see the psu close to the middle of the "rack" for example processor no more than 3 modules away and distance for an io module might be no more 8 modules from psu
the power supply requirements is based on the power requirements of the modules the power supply is powering. You can have multiple power supplies in the same rack.
Local modules means connected to the local rack the same rack the CPU is installed in.
Ethernet I/O would all be classified as remote and the max number would depend on the processor limits am in case of multiple I/O networks each network would have a limit of the max for a subnet. I think it's about 250 I try to limit my number to less than 200 incase I need to add 1 or so.
You can Bank on it...
GaryS said:
the power supply requirements is based on the power requirements of the modules the power supply is powering. You can have multiple power supplies in the same rack...
GaryS,
If by "rack" you mean CompactLogix "Bank", then that would not be correct. You may only have one 1769 Power Supply per Bank.
For a 1769 based CompactLogix System...
Bank 0 may only have one 1769 Power Supply.
The controller must reside in Slot 0.
There can be a maximum 3 x I/O modules between the controller and the 1769 Power Supply.
On the other side of the 1769 Power supply there can be a maximum of 8 x I/O modules.
Therefore, the maximum number of I/O modules for Bank 0 = 11
Any more than 11 x I/O modules in Bank 0 is invalid.
If a 1769 CompactLogix System requires more than 11 x I/O modules then a new Bank must be created with its own 1769 Power Supply. Additional Banks, and their 1769 Power Supply, must be connected together with one of the 1769 expansion cables.
Bank 1 does not have a controller in Slot 0
Therefore, for controllers that support the maximum of 30 I/O modules (certain L3x controllers)...
Bank 1 may have a maximum of 8 x I/O modules either side of a 1769 Power Supply.
Therefore, Bank 1 may have a maximum of 16 x I/O modules in total.
Any more than 16 x I/O modules in Bank 1 is invalid.
Bank 0 = 11
Bank 1 = 16
Total so far = 27 x I/O modules
So, Bank 2 may then only have 3 x I/O modules, reaching the total of 30 x I/O modules for the entire System.
Bank 2 also requires a separate 1769 Power Supply.
Any more than 3 x I/O modules in Bank 2 is invalid.
Other CompactLogix controllers support less Banks and less maximum I/O modules per System.
The above is an example outlay of a maximum of 30 x I/O modules. The actual maximum will be determined, and as mentioned, by the 1769 Power Supplies used and their current capacity. Also, by the I/O modules selected and their current draw and minimum distance rating to the Power Supply in their Bank.
To recap: A second 1769 Power Supply cannot be added to any Bank for additional power, but may be added with a new Bank and extension cable. Each Bank's Power Supply only provides power for that Bank. It cannot provide additional power to adjacent Banks.
GaryS said:
...Local modules means connected to the local rack the same rack the CPU is installed in...
Or, a local module may be an I/O module that is installed in an additional Bank, where no controller is installed i.e. any of the possible maximum 3 x Banks.
GaryS said:
...Ethernet I/O would all be classified as remote and the max number would depend on the processor limits...
For the newer CompactLogix controllers, the number of Ethernet devices added to a System are counted as "Nodes". Each controller has a Node limit. Only Ethernet device that are added to the project's I/O Configuration are counted against the Node limit. These are indeed external devices and have nothing to do with the local I/O modules added to Bank 0, or subsequent Banks, if applicable.
GaryS said:
...in case of multiple I/O networks each network would have a limit of the max for a subnet. I think it's about 250 I try to limit my number to less than 200 incase I need to add 1 or so.
Modern Industrial Automation and Control Systems (IACS), utilizing Converged Plantwide Ethernet (CPwE) architecture, do not conform to the Ethernet standards of old, such as those used in Domestic and commercial settings, where IP addresses are dished out within one range until there are no more. In CPwE, Segregation is achieved primarily using IP Subnets and VLANs. By designing the overall system into individual Cells/Zones, you greatly reduce the number of nodes per Subnet or VLAN. A properly designed and segregated CPwE architecture will typically not have IP addressing assigned up into the hundreds. In fact, within several relatively small Cell/Zone areas, it is quite common to see the same IP Subnet range used repeatedly. NAT appliances are then used to translate the Cell/Zone addressing to the wider network.
By today's IACS standards, you do not keep assigning Plantwide 192.x Class C addresses up into the hundreds and beyond. I still see lots and lots of references to users implementing "Office" Ethernet standards in Industrial settings, using 192.x Class C addressing where networking appliances, such as routers, typically allow up to 254 devices to be connected together. 10.x Class A addressing is more the norm for Industrial CPwE architectures where you want to introduce multiple Subnets/VLANs, each facilitating up to 254 devices, or Nodes, each, but typically not reaching anywhere near that limit.
This is not a "you must do this" lesson. It's just how it's done nowadays and what is considered good practice and the industry norm.
Regards,
George
Hi labeledas,
Trust me. I have nowhere near a fraction of the time I would like to contribute here more often. There are so many posts I read where I feel I have something to give, point out, or correct, but just cannot afford the time to do them justice. When I do find some time, like this week, I like to pick certain threads, especially ones where someone is seeking or misunderstanding the fundamentals of the topic of discussion. Fundamental understanding, I believe, is the foundation for success.
I also don't like to rattle off many quick one line posts where I feel that more detail or explanation will best serve the reader or readers.
With regard to "post count" here on the Forum, "Quality, not quantity" is my motto.
Regards,
George
I am working on a project using a NB screen and NX1P2 PLC. I am having a really hard time getting a real number to properly translate through to...
122
Complete noob here, using a Click C0-02DD1-D to run a test stand. Requirement is to turn on motor run for X seconds, turn off and dwell for X...
1,095
Hi, I have this weird issue whenever I try to change the SNN from a Point IO Im missing the three ... dots to open the pop up and change it...
621
I'm doing my first PanelView 5000 application with Logix View Designer v8, and am of course jumping in headfirst. One thing I don't find is a way...
705
Hi PLCs.net! I was curious: How many axis can a B&R APC910 control? Is there a hard limit like certain AB controllers? I'm new to B&R, so would...
373