Old school-Modicon 984-685E Hot Stand-By Question

rivas1464

Member
Join Date
Dec 2003
Posts
1
I've got an existing Modicon 984-684E system set-up in a hot stand-by configuration. The customer tried to add a couple of new I/O cards with disasterous results. The system was down for a half hour before they could get it back up and the new I/O cards were not active. I haven't used a PLC like that in over 10 years and I've forgotten how to deal with an I/O configuration change on a hot stand-by system with minimal impact. I know how to download a new program with no problem but I'm unsure about I/O config changes.

I'm guessing you need to stop the secondary PLC, make the I/O config changes, then kill the primary and then bring up the secondary with the primary off line. Then make the same changes to the primary and bring it back up on-line.

Any help?

Thanks.
 
I agree.

For new I/O to be recognized, the processor Traffic Cop needs to be edited. This requires a "re-configuration" of the processor so it must be done Off-Line.

Caution: an error might be generated when your primary processor ladder logic is not equal to your stand-by processor logic. The processors don't really care however some component in your system may be monitoring the Hot-Standby (HSBY) status register bit 12
 

Similar Topics

I've got an old WinCC project and I'm trying to check what tag address certain values relate to. I have a screen that refers to...
Replies
5
Views
2,219
Hello All, So i ran across the TI505 PLC from Texas instruments, which is under Siemens now. This is a very old PLC, and as simple as it may...
Replies
13
Views
3,747
You know who you are... ;) My customer has an old cartoner run by an Omron S6 (3G2S6-CPU15), with two ID-411 input modules, and two OC-221 output...
Replies
6
Views
2,457
I want to connect three PLCs together. I have two SLC 5/03s. One with an available serial port, and one with an available DH485 port. And one...
Replies
2
Views
4,079
On the old school SLC 500 brick...the port on the front that looks like an RJ45 port, is that a DH-485 port like what I would find on a SLC 5/03...
Replies
2
Views
3,188
Back
Top Bottom