Dear All,
I require valuable suggestion for solving below mention problems.
I’m using Omron PLC Analog module AD041 for scaling pressure switch (0-15PSIG = 0.5-4.5VDC)
I’m using SCL scaling instruction
SCL : S = Source word = Analog Input Add ( 5)
P1 =Scaled value for point A ( 0 PSIG)
P1+1 =Unscaled value for point A ( 603 Analog counts at 0.5VDC)
P1+2 =Scaled value for point B ( 15 PSIG )
P1+2=Unscaled value for point B ( 5500 Analog counts at 4.5VDC)
But I’m not getting scaled output from the SCL (Result word )
Please let me what could be the problem in program…
Attached is the program ladder fro your reference..
Thanks!