Omron output relay problem
Check PD022 for bent, missing, broken, or retracted pins.
You have connected an external 24VDC supply to the (DC 24V input terminals) of your PD022, and the PD022
POWER Indicator is ON, correct?
A belated Welcome to the Forum!
alphatargets said:
...At the moment I have just the CPU and the output module connected...
You haven't mentioned it and no one else has asked yet, but are you fitting a CJ1W-TER01 Terminating End Cover to the right of the Output module while you are testing? This must be fitted to terminate the bus.
Regards,
George
Regards,
George
Hi Geospark, yes the end cover is fitted and I have tried a replacement just in case. The only thing that has not been replaced is the power supply, and I should be able to pick one up tomorrow
Solved
So in the end this whole thing was down to a faulty Omron CJ1W-PD022 power supply unit which was not providing the 24v required to power the coils of the relays.
Thanks to everyone for your time and contributions.
Wow! That is really rare! Have never had one fail although I do not use AC power supplies only ever DC with a separate switchmode to power the lot.
Rare indeed.
However I recently experienced one faulty CJ1W-PA202 AC power supply out of an order of 40 units. It was immediately exchanged by OMRON under a very efficient RMA system.(y)
I have PLC Omron CJ2M with OD211 module. I want to use the pulse output and PWM output and this module. But i confuse how to activated this, i...
136
I have a project to control the speed of motor DC using PWM Output on PLC and when im on working i have a several trouble and of of them is the...
272
Hi, I'm using CX Programmer and just seeing what the best way to trigger an output from the plc clock time would be. I need this to come on at 9am...
1,785
The plc output donot work sometime although condition is true. I have seen a difference in activation sign while in online mode as seen in the...
1,778
Hello Sir/Ma'am, Hope you and your family are safe in this Covin-19 Pandemic. One of my client have a machine in their ceramic industry which...
2,643