Thank you ALL for your feedback. I got my Thermocouples from OMEGA today and was able to run a quick test at room temperature.
1. Thermocouple with 36" lead directly terminated at PLC TC Card.
2.Thermocouple with 36" lead + 24" extension wire connected via a a standard set of terminal blocks, but connected to the same screw terminals, and then the extension leads terminated at PLC TC Card.
Both sensing elements were placed next to each other in a room. After an hour or so,
#1 Read 22.12 Degrees C
#2 Read 22.10 Degrees C
I could have gone with longer lead lengths, but to get one in custom lead lengths, there was a 26 week long lead-time. At some point, I would like to do a test where the test would ramp up to temperatures in excess of 100 C and see what the delta might be with hook-up #1 & #2. Unfortunately, that would have to be at a later date as I do not have the luxury of a spare TC card at the moment and the system that this is going in to, has no provision to attach a 2nd TC.
NATHAN,
Thanks for the OMEGA links. I swear, sometimes searching thru Omega can be challenging. They won't bring up some of their own stuff during a search.I specially like the din-rail mount that accepts the plug. If they have that in stock and I can get it within a week, I will go that route.
Thanks again to all of you for your help. A Happy Thanksgiving to all of you and your families.