Ken Roach
Lifetime Supporting Member + Moderator
In this case, with a 1747-SCNR and ControlNet PanelView, you get access only to the ControlNet-Scheduled connection data.
The 1747-KFC15 would give you random access to any data table in the SLC-5/03. That's why the SCNR and KFC15 were often used together.
You might have access also to CIP Assembly objects; I'd have to look at that specifically.
The 1747-KFC15 would give you random access to any data table in the SLC-5/03. That's why the SCNR and KFC15 were often used together.
You might have access also to CIP Assembly objects; I'd have to look at that specifically.