Hi..
I used Panelview Plus 1500 with DH+ to PLC-5/25 and set alarm triggered using bit type, 4 word, tag on RSView Studio is
::[PVP]B15:0,L4
Tag type analog with integer format, minimum tag is -32768 and maximum 32767.
I have a problem with no alarm banner displayed, no alarm list when an alarm triggered, no error message on PV+.
How to solve above problem? Any idea?
Thank you.
James
There seems to be a mismatch between the tag type selected and the tag you are using for alarms.
If the tag you are monitoring is a bit (or array), but the alarm trigger is set for value, I don't believe your alarm will trigger.
I suggest trying to set the alarm trigger to bit, as a starting point...