PanelView Plus 1500 won't change default application
Canada_Joe
Jan 2013
Burlington
Hello,
I am using FactoryTalk View Studio to design an application to be used on a PanelView Plus 1500. This panel has been used before and a I believe a slight error has been carried over.
On startup if I set it to run an application I will receive the message "ERROR: Runtime file not found at '\Storage Card2\Burnin04.mer' Please verify the correct file name was given" and then I can go to the configuration screen. This will happen whether I go into terminal settings and set it to run the current application at startup or if I download and application and select that it runs at startup.
It seems like it is unable to change the path of the application to run at startup. I am very new to using this software and nothing I've tried has worked. Any help would be greatly appreciated.
The Burn-in MER is a factory test program, so this terminal is probably brand new. It ought to be replaced by the "current application" but in some cases it's not.
RA Knowledgebase Article ID 190128 suggests that you need to perform a factory defaults action on the terminal as follows:
Reset the terminal to defaults using the following procedure:
Connect a USB keyboard to the PVP6 logic module.
Boot the PVP6 into Maintenance Mode by pressing the default button on the back of the logic module.
Press the down arrow to select Special BOOT Action.
With this option selected, press the right or left arrow keys until Special BOOT Action - Restore Factory Defaults is selected.
Press the up arrow to select Continue booting with selected options.
Press the Enter key to continue booting.
89
Hi there, Maybe I am overthinking this issue, but here is what I have going on. I have a program running for a water valve on a DI system. We...
451
Hi guys. Currently working on a project that requires a Panelview Plus 1500 to read a CSV File (recipe) from a network drive. The issue I have...
1,063
Hi, guys, how’s going? I added one “Trend Object” on screen A in PanelView Plus 1500. Then configured “Refresh Rate”, “Buffer” ……and set up...
1,916
Good morning, I am onsite at a customer. They have a panel view plus 1500 that does not light up. The screen is always black. I am not very...
5,576