Idaho Project Panelview + and DH+ comm
Hello, I am the systems integrator on this project. This is the first time I have used this message board and I am very pleased with the amount of ideas and knowledge available, and thank you very much for all your comments.
The system DH+ architecture contains (8) SLC/5/04's including the blower PLC, (1) Panelview +, (1) RSView 7.00 SCADA Node, (1) RSView 32 7.00 Works Development Node.
The DH+ network has been verified that it is NOT a star configuration, that it is a daisy chain network, and there are termination resistors at each end.
When the Blue and Clear wires on the PV+ are backwards as described above the DH+ network crashes completely, every PLC in the RSWho window gets a red X.
When the Blower PLC and PV+ is wired properly into the DH+ network, the DH+ connections in the RSWho window will frequently show a red X, come and go, not always the same PLC and always one or more PLC's with a red X. RSView32 crashes and locks up completely, no screen display of any data points.
At this point we have to bypass the PV+, close the RSView32 SCADA project and restart in order for RSView32 communication to work again.
Maybe this inforamtion will stir up some more ideas.
Thanks