Recently we had a PanelView 1000 go out on us. Processor still working, thought it was just a bad back light.

We installed a new one and all went OK, but every now and then the screen gets jumpy. It is a 100-240VAC unit and the 120VAC looks OK.

Could an issue with the Ethernet connection cause this? (It is connected to a pair of SLC 500s through a Ethernet connections.

Any other thoughts?

Anything would help. Thanks in advance and may everyone on PLC.net have a good Holiday Season.
 
From your description, I'd say you're looking at a slow cascade of failures on the video board. First the high voltage supply for the backlight tubes, now something failing in the video driver circuitry.

The PV1000 was the most popular of the large PanelView Standard models, so there are a relatively large number of them available on the aftermarket, but RA isn't making parts for them anymore.

If it were my terminal, I'd be working on a conversion to PanelView Plus or planning a conversion to another hardware and software platform.
 
Hi,
I have seen many of these hmi screens fail in this fashion over the years. Screen eventually fails completely and this model is no longer supported by AB.

I would agree with Ken and begin a plan to convert the application to PV+ and upgrade the hmi.

Regards,
Donnacha
 

Similar Topics

Hi there, Maybe I am overthinking this issue, but here is what I have going on. I have a program running for a water valve on a DI system. We...
Replies
4
Views
455
Got a problem on an install this weekend I'm hoping someone can help out on. I'm upgrading an old system with a SLC5/04 and Panelview 600...
Replies
3
Views
1,140
I have a Panelview Plus 1000, keypad only that has an annoying problem that I hope someone can identify. Recently, every time an application is...
Replies
4
Views
753
I am using FactoryTalk View 8.1 and restored a 6.1 .mer file. When the .mer file is loaded into a PanelView it starts up with the Main Menu and...
Replies
8
Views
1,638
Hi all, I have an ihm and I need to connect this with compact logix PLC. In factory talk this communication works well (factory talk and fisical...
Replies
1
Views
2,343
Back
Top Bottom