panelview remote opc server
ygnm
Feb 2015
vicksburg, ms
85
hey guys. i am having an issue and maybe somebody here can help me out with it. i have a panelview plus that i am trying to get to read kepserver from a remote opc server. i have everything set up and when i run it on my computer it works find but it says the item is no longer available when i run it on the the panelview itself. i think part of the reason maybe that when i navigate to the computer that its hosted on to set up the server it looks for it by the computer name. i'm not sure if the panelview plus can do that. i'm kind of stumped right now. any help anybody can give will be greatly appreciated. thank you in advance.
No, PanelView Plus cannot do that (connect to remote OPC server).
What you can do is a bit tricky:
1) Setup your PVP project to use Kepware Modbus Ethernet
2) Setup the Kepware Modbus Ethernet driver to read/write from a remote Modbus Ethernet
3) Make your remote Modbus Ethernet device a Kepware OPC server
You can also use that trick to have two PanelView Plus devices share data. Just setup one of the PVP with Kepware as the Modbus master.
It will work on the desktop; using FTView ME Station.
It would be awesome if the PanelView Plus could talk to a network FactoryTalk Data Server, or remote OPC server. But that does not work when running on the PanelView Plus.
When we use PVP connected to Siemens PLC, it uses kepware for communication. I install the OPC on my development PC, set up the tags etc and then import them to the screen.
Can you use the internal OPC server as well? In other words, copy the setup from your remote server, and import it to the on-board kepware server?
if i set everything up in kepserver enterprise it polls the data fine. the issue is that enterprise doesnt have the abb totalflow native addressing and not all of these totalflow's have had modbus addresses set up in them and i am not allowed to access them and set them up. like i say when i run it from my laptop its fine but once i put it on the panelview itself its a no go.
Hello, I presently have a Allen Bradley PanelView 5310 at a client site and i can access to the PLC/HMI local network with a remote module...
104
Hello, I have a machine with a 1756-L72 Controllogix PLC and 1756-EN2T network card, and PanelView Plus 7 HMI. I am using RSLogix V20.05.00...
904
I am trying to copy a .csv file from a PanelView's SD card onto a a remote windows server. I understand that the panelview does not allow you to...
2,176
Greetings. I have a project in PanelView Plus 1000, that cosist in datalogging some variables using the ActiveX object DataStorePlus. For that...
1,457
Hi, I am setting up a technical manual display page on a PANELVIEW PLUS 1250 HMI, and the page references .pdf files held on an SD card on the...
1,664