Panelview Standard 2711-T6C8L1 Locked/password
Microbictomb
Mar 2015
Michigan
56
Ser. B Rev C FRN 4.43
Anyone happen to know if you can reset the password on these, we bought one used in unknown condition except that it powers up, well it does turn on but there's a password locking it up.
I'm really hoping I can jumper a couple points on the board and set it back to factory default or something if anyone can help please... :unsure:
Communications will not work and there is no config screen selection on start up, whoever wrote the last program failed to add a button for config. The start up screen has one button that says "Main" for main screen I'm assuming but it asks for the password when you select it as well.
Look for a white square in the corner of the touchscreen during powerup; press it when it appears.
That ought to get you to the Configuration screen.
A firmware update via Flash card might do the job too.
You should be able to download without having to be on the config screen. At least have always been able to so.
Communications will not work and there is no config screen selection on start up, password when you
Do you know why you can't connect.
How do you have RSLinx setup? Are you using a straight thru cable?
If the Aux/printer port is set for a printer then that could be the reason. That can be changed when you get to the configuration screen.
So I am have bad day or I have just something I can not see I have 3 standard PV's T6C5L1 this is a RS232 (DH485) one port, I can download or...
4,305
Had an interesting experience this morning. An old Panelview 600, 2711-K6C5X series B to be precise, comes up as error 32. Unfortunately it...
215
Good evening. I am in serious need of help. I am trying to connect a Panelview Plus 7 Standard to a SLC5/03(1741-L531) using a Moxa MGate...
646
Good evening. I am trying to get a SLC 5/03 connected to a Panelview Plus 7 Standard using a Moxa Mgate EIP3170 and I am not having much luck. I...
529
Hello, We have an older machine that has a standard PanelView (2711-T10C3) connected over DH485 to a SLC 5/04 PLC via a 1761-NET-AIC module in...
681