Hello,
Have a ML1000 communication via NET ENI module to a PanelView Plus 600 HMI running Ver3.1 firmware.
In my FTView 6 I've created and on line project file and can see the ML1000 variable.
When I try to access integer variable in HMI using 'Numeric Display Button' and following Tag config:
{::[TB1_PV_Corona1]N7:30.1}
I always retrieve 0.
My FT View 6 verifier of connect continues to talk of acd and not rss file. But I presume this is incorrect as I can read variables in Online Tag folder. (see attachment)
Any suggestions appreciated.
{::[TB1_PV_Corona1]N7:30.1} refers to the second bit (.1) of a 16-bit integer Word.
{::[TB1_PV_Corona1]N7:30} refers to the whole integer value. That's what you want in a Numeric Indicator object.
The Offline Tag Browsing feature only works with RSLogix 5000 project files (*.ACD), and not with PLC-5 or SLC-500 project files.
That's why you can browse the data files online, or manually type in data file addresses, but you can't browse the data files offline.
If you delete the offline tag path from that field, the verifier won't complain about it.
Addressing MicroLogix1000 variable from PanelViewplus firmware version 3.1 & FTView 6
Thanks Ken.
Am not at work to check on the processor now.
But was also having problems addressing the individual bits on the MicroLogix1000 via FTView.
I believe in the RS500 I was programming a certain address as b3.0/1 & it behaved as expected.
FTView was forcing me to write the syntax as {::[TB1_PV_Corona1]B:3.0.0} to address the individual bit b3.0/1, BUT I still could not toggle that bit from FTView application program.
is there a good link or documentation that outlines FTView 6 syntax to write to ML1000 variables ( when using Panelview plus as hardware ) ??
Thanks,
E
Hello Ken,
FYI
When I programmed the bit address as {::[CoronaTB1]B3:0/3} in FTView Ver 6 for a PanelView Plus , it was recognised in my ML1000 PLC
E
Hello Everyone, I am setting up an Information message in FactoryTalkView ME. I'm just using the default information display. I want to make it...
873
Hello to the community, I am new to Rockwell and I have a small problem with a PvP1000(2711P). Some buttons in the same screen are not...
2,374
Hello, I have a PV+ 1000 that I am unable to access the config screen on. All I want to do is upload the .mer that is currently running. I tried...
21
5,077
If you were to take a Panelview Plus, mount that in an enclosure that is purged by a purge unit that takes the environment from Class 1 Division 1...
5,693
So im working on a little something i was hoping to get some advice on. I have a PanelviewPlus 7 that will be using the MECSVLog ActiveX on to...
1,252