Palnivelmoorthy87
Member
Hi
I am using CPU 317-2DP..Its a Software Redundancy..
One of the Station(PLC1) is working properly,But Station B(PLC2) is in STOP Mode...I Cant able to put it in Start mode..
I have attached my Diagonistic buffer..Its very urgent
Diagnostic buffer of module CPU 318-2
Order No./ Description Component Version
6ES7 318-2AJ00-0AB0 Hardware 3
- - - Firmware V 1.2.1
Rack: 0
Slot: 2
Event 1 of 100: Event ID 16# 5371
Distributed I/Os: End of the synchronization with a DP master/IO controller on slot 2
Number of distributed stations: 2
Priority class: 22
Incoming event
02:12:56.662 PM 01/31/2004
(Coding: 16# 5371 1602 0050 0002 0000 0000)
Event 2 of 100: Event ID 16# 530D
New startup information in STOP mode
Startup prevented by:
Loading user program or internal inconsistency detected
(SDBs less than 200 incomplete, superfluous, or incorrect)
User program invalid
- STOP request exists
- Cold restart or warm restart necessary
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of automatic startup type at power on:
- No startup type/following memory reset
Operating mode: STOP (internal)
Incoming event
02:12:54.425 PM 01/31/2004
(Coding: 16# 530D FF04 C777 0341 0810 0100)
Event 3 of 100: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 1007
Previous operating mode: STOP (internal)
Requested operating mode: STOP (internal)
External error, Incoming event
02:10:05.011 PM 01/31/2004
(Coding: 16# 49A0 FF44 007B 03EF 2A02 0B00)
Event 4 of 100: Event ID 16# 6547
Parameter assignment error assigning parameters to modules (not on P bus, cancel download)
no relevance for user: SDB number: 1007
Operating mode: STOP (internal)
Internal error, Incoming event
02:10:04.999 PM 01/31/2004
(Coding: 16# 6547 FF04 007B 03EF 0000 0000)
Event 5 of 100: Event ID 16# 5371
Distributed I/Os: End of the synchronization with a DP master/IO controller on slot 2
Number of distributed stations: 2
Priority class: 22
Incoming event
02:09:57.359 PM 01/31/2004
(Coding: 16# 5371 1602 0050 0002 0000 0000)
Event 6 of 100: Event ID 16# 4303
STOP caused by stop switch being activated
Previous operating mode: STOP (internal)
Requested operating mode: STOP (internal)
Incoming event
02:09:55.005 PM 01/31/2004
(Coding: 16# 4303 FF44 0000 0000 0000 0000)
Event 7 of 100: Event ID 16# 4300
Power on backed up
Initialization information: Initialization after power on (backed up CPU)
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
02:09:47.384 PM 01/31/2004
(Coding: 16# 4300 FFF3 CE00 0000 0001 0000)
Event 8 of 100: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
02:09:41.366 PM 01/31/2004
(Coding: 16# 494E FF4F 0000 0000 0000 0000)
Event 9 of 100: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 1007
Previous operating mode: STOP (internal)
Requested operating mode: STOP (internal)
External error, Incoming event
02:02:28.438 PM 01/31/2004
(Coding: 16# 49A0 FF44 007B 03EF 2A02 0B00)
I am using CPU 317-2DP..Its a Software Redundancy..
One of the Station(PLC1) is working properly,But Station B(PLC2) is in STOP Mode...I Cant able to put it in Start mode..
I have attached my Diagonistic buffer..Its very urgent
Diagnostic buffer of module CPU 318-2
Order No./ Description Component Version
6ES7 318-2AJ00-0AB0 Hardware 3
- - - Firmware V 1.2.1
Rack: 0
Slot: 2
Event 1 of 100: Event ID 16# 5371
Distributed I/Os: End of the synchronization with a DP master/IO controller on slot 2
Number of distributed stations: 2
Priority class: 22
Incoming event
02:12:56.662 PM 01/31/2004
(Coding: 16# 5371 1602 0050 0002 0000 0000)
Event 2 of 100: Event ID 16# 530D
New startup information in STOP mode
Startup prevented by:
Loading user program or internal inconsistency detected
(SDBs less than 200 incomplete, superfluous, or incorrect)
User program invalid
- STOP request exists
- Cold restart or warm restart necessary
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of automatic startup type at power on:
- No startup type/following memory reset
Operating mode: STOP (internal)
Incoming event
02:12:54.425 PM 01/31/2004
(Coding: 16# 530D FF04 C777 0341 0810 0100)
Event 3 of 100: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 1007
Previous operating mode: STOP (internal)
Requested operating mode: STOP (internal)
External error, Incoming event
02:10:05.011 PM 01/31/2004
(Coding: 16# 49A0 FF44 007B 03EF 2A02 0B00)
Event 4 of 100: Event ID 16# 6547
Parameter assignment error assigning parameters to modules (not on P bus, cancel download)
no relevance for user: SDB number: 1007
Operating mode: STOP (internal)
Internal error, Incoming event
02:10:04.999 PM 01/31/2004
(Coding: 16# 6547 FF04 007B 03EF 0000 0000)
Event 5 of 100: Event ID 16# 5371
Distributed I/Os: End of the synchronization with a DP master/IO controller on slot 2
Number of distributed stations: 2
Priority class: 22
Incoming event
02:09:57.359 PM 01/31/2004
(Coding: 16# 5371 1602 0050 0002 0000 0000)
Event 6 of 100: Event ID 16# 4303
STOP caused by stop switch being activated
Previous operating mode: STOP (internal)
Requested operating mode: STOP (internal)
Incoming event
02:09:55.005 PM 01/31/2004
(Coding: 16# 4303 FF44 0000 0000 0000 0000)
Event 7 of 100: Event ID 16# 4300
Power on backed up
Initialization information: Initialization after power on (backed up CPU)
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
02:09:47.384 PM 01/31/2004
(Coding: 16# 4300 FFF3 CE00 0000 0001 0000)
Event 8 of 100: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
02:09:41.366 PM 01/31/2004
(Coding: 16# 494E FF4F 0000 0000 0000 0000)
Event 9 of 100: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 1007
Previous operating mode: STOP (internal)
Requested operating mode: STOP (internal)
External error, Incoming event
02:02:28.438 PM 01/31/2004
(Coding: 16# 49A0 FF44 007B 03EF 2A02 0B00)