We are having a problem with slow communication between the HMI (Parker CTC P11-314DR) and a SLC 5/04 using DF1-Full Duplex.
This problem has existed "for years" according to one of my technicians.
I believe I have identified the problem which is a serial cable about 100' long with at least two sets of terminal blocks, one in the PLC panel, and another on the semi-portable machine.
But, I have a couple of questions about the Parker CTC HMI:
1. Machine Shop Software: I found a folder with all the setup files for the software stashed away on a shared drive. I installed it on my desktop. I can open the software, and open the project, but the New Project button is greyed out, and I can't see any of the project settings other than description. Am I missing a license or activation of some sort? Or are there other bits and pieces I need to install?
2. Serial port settings: Our SLC serial port is set as follows:
DF1 Full Duplex
19200 Baud
Parity NONE
Stop Bits 1
No Handshaking
BCC Error detection
Embedded Responses Enabled
Those last two items I am most concerned with. I am not sure if the OEM set it up that way to try to overcome the problems caused by having a serial cable that is about twice the recommended length, or if those are typical setttings used with this particular HMI.
Tomorrow, the machine will be down, and I will see what I can do to shorten the serial cable. The machine is running fine, but the response to/from the touchscreen is very slow and the screen is occasionally populated with "!" where values should appear.
Thanks in advance.
Paul
This problem has existed "for years" according to one of my technicians.
I believe I have identified the problem which is a serial cable about 100' long with at least two sets of terminal blocks, one in the PLC panel, and another on the semi-portable machine.
But, I have a couple of questions about the Parker CTC HMI:
1. Machine Shop Software: I found a folder with all the setup files for the software stashed away on a shared drive. I installed it on my desktop. I can open the software, and open the project, but the New Project button is greyed out, and I can't see any of the project settings other than description. Am I missing a license or activation of some sort? Or are there other bits and pieces I need to install?
2. Serial port settings: Our SLC serial port is set as follows:
DF1 Full Duplex
19200 Baud
Parity NONE
Stop Bits 1
No Handshaking
BCC Error detection
Embedded Responses Enabled
Those last two items I am most concerned with. I am not sure if the OEM set it up that way to try to overcome the problems caused by having a serial cable that is about twice the recommended length, or if those are typical setttings used with this particular HMI.
Tomorrow, the machine will be down, and I will see what I can do to shorten the serial cable. The machine is running fine, but the response to/from the touchscreen is very slow and the screen is occasionally populated with "!" where values should appear.
Thanks in advance.