Pilz safety relay
Amy_Fields
Aug 2013
Toronto
30
I will be re-wiring a dual palm out station and replacing with 1 palm out PB. These two PB's are tied into a pilz x3 774350 start switch safety relay. If I go with an AB 800z style pb (1) and tie the outputit into s11 or s21 on the pilz safety relay, and put in a jumper between s11 and s21 will it still function the same way?
Thank you.
Thank you.
Do you mean this unit - P2HZ_X3 ??
Then the answer is No.
Look at the data sheet.
http://www.pilz.com/downloads/open/P2HZ_X3_Data_sheet_1002153-EN-02.pdf
You will see that the device's input is - "Two-hand button
with detection of shorts across contacts"
Why would you want to do this - what does your risk assessment say?
Yes, I am referring to the P2HZ_X3. Light curtains have been added to the cell and a dual palm out station is no longer necessary. Thank you for the reply I appreciate it.
Even with light curtains. Why does the operator need one hand free?
The previous mechanical guard is the only change.
What happens if the light curtain fails
You call
I have a banner dual touch run bar (replacing an older dual palm button station) which I am trying to tie into a pilz safety relay (Pilz p2hz x3)...
2,812
My plant is going through an upgrade, a 3rd party are proposing a PILZ programmable saftey system (not sure of model) which will have comms on...
2,170
Hello Everbody. We are going to be performing a revamping project on an existing plant. In the mean time we are going to upgrade the "old" Pilz...
2,835
Does anyone have a link to the latest "Guide to Machinery Safety" from Pilz? I see many references to it online and they all say it can be...
4,920
Hi Guys, I'm trying to integrate Pilz Ethernet IP Module to ControlLogix. I added Pilz module as a Generic Ethernet module and I'm able to...
523