Hi all.
I have never given grounding much thought, apart from that there must be a "good" grounding covering the entire plant.
I though that a 16mm2 wire all around was most common.
Actually I am confused about the requirements for the earth wire size. An earth wire in a cable that leads a current is sized together with the cable. But what about an equipotential earth ?
Now, we have a subsupplier that specifies a 30mm x 3.5mm galvanized bar to protrude 1 meter from the floor in various strategic places.
The subsuppliers system is hefty inverter system for a melting furnace. So maybe the requirements for grounding is specially severe in this case.
Questions:
Does anyone else use grounding in this dimension ?
Any good source for standards for grounding and equipotential bonding ?
Any suppliers of the stuff ? I would like to find one that actually supplies 30mm x 3.5mm galvanized bars for this purpose.
Looks normal for me. We work alot in Ex zones.
Then customers provides this bars arround to factory so we can earth our equimpent to it.
I don't know if it is 30*3 but we mostly have 35mm² earthning providied to it, at the picture the steal bar that comes out of the ground.
And you connect with 16mm²
Thanks guys, yes that looks like it fits the bill !
You wouldnt know where to look for this stuff ?
I guess that if you work with electrical installations in buildings it is trivial, but for me is not normal.
I asked this question in the States recently when I realised there was no earthing between conveyors, I was looked at daft and told don't be silly, they are metal and connected together and in any case the conduits (yes they use this abundance) give an earthing route.
This is standard and to my knowledge a must in german buildings. You may also find it as protection against lightning as lightning conductor.
Jesper
There is a British company called Furse who specialise in earthing and lightning protection. They might be worth a look.
You should see the earthing requirements aroud a power or sub station. Earth rods everywhere at 2 metre intervals - a grid if you like, all joined together with copper wire. Half the time you also have to use Bentonite and water down the holes to get the required resistance.
Management has decided they want a monitoring screen for every PLC and IO module in the plant. Also looking for a way to monitor when a PLC fails...
1,373
Wow, did you see the terrible accident in Seattle: http://www.bloomberg.com/apps/news?pid=20601087&sid=argFhVY_qDA8&refer=home I'll bet I'm...
1,721
Hi all, I'm connecting several 4-20mA sensors together in parallel (only one shown below) The enclosure is ABS plastic with metal backplate DAQ...
307
I have Rhino 120 to 24 dc power supply and it has 2 Positive and 2 negative terminals on the DC side but no ground terminal. Should I connect one...
451
Hi, Our customer has bought a machine a CNC wood cutting machine. It states that it need a seperate 16mm2 EMV"ground" in addition to our 5G16mm2...
610