The curve defines the delay in time before the breaker tripps. The general rule I use is Motors= D curve, Electronics = B curve.Hey all should I use C Curve or D Curve circuit breaker? What does that mean?
Thanks
Can the Breakers be installed right next to each other? And can they be right next to the power distribution block? Like less then an inch apart?
Can the DIN mounted Double-level terminal block be mounted next to the relays? I did order separators for the terminal blocks. I think I have plenty room if I need to have space. I am going to place an order tomorrow, should I post a list of what I am ordering? I am buying stuff for the greenhouse relay box. I will be buying enough relays and terminal blocks for the whole system, but am just building one relay box.
Relays Can be mounted side by side no gap needed. Generally anything DIN rail mounted does not need a Gap. The exceeption to this rule is PLC's and DC Power supplies. Unless you see a vent on the side of the device and it is DIn rail mountable then no spacing needed.
Posting your list would help. Since you have been ao the Automatiin Direct web sight, take a look at the 22mm switches. These are NEMA4X rated. Since you want to start this project basically as 'relay logic" then these switch will be handy. Also they are pretty cheap.