In the circumstances shown in my drawings, I do not use fuses or circuit breakers at all as the switch mode power supply turns itself off if something goes wrong.
I also do not ground the negative output from the switch mode as this destroys the isolation properties of the power supply.
If feeding from batteries with potentially high currents I use Schneider circuit breakers for input and output supplies, despite the fact that I also use 24VDC/24VDC switch mode power supplies between the batteries and the PLC. A lot depends on what the customer is prepared to pay. Once again no grounding of the negative output from the switch mode. Let it float - no problems as there is no ground reference.
I also do not ground the negative output from the switch mode as this destroys the isolation properties of the power supply.
If feeding from batteries with potentially high currents I use Schneider circuit breakers for input and output supplies, despite the fact that I also use 24VDC/24VDC switch mode power supplies between the batteries and the PLC. A lot depends on what the customer is prepared to pay. Once again no grounding of the negative output from the switch mode. Let it float - no problems as there is no ground reference.