PLC Ethernet/IP Network Layout Suggestions
Did not know about Gamechanger. Thahnks for the information.
Stratix 5700 is of course a very good product. Has DLR supervisor capability if I remember correctly up to three independent rings. It also has some fiber ports. You should have no problem setting the device-level rings for the armour blocks that you mention this installation requires.
Decided to separate PLC from other cabinets. This gives the ability for any station to be completely locked out without affecting others. I can also avoid using stratix's and go for unmanaged switches. In this config the cables will be under 50m long.
OK, so you have a ControlLogix and can have multiple EtherNet/IP modules. The applications on the factory side need only access tags in the PLC and not directly to VFDs, I assume. I think this configuration is suitable for your requirements. Good luck with the project.
Thank you.
I can access VFD parameters via PLC Ethernet I/P
dlr via etaps is probably cheaper and simpler, but he mentioned being able to lock systems out
I did not consider that option because... it seems useless to me. The two network cables will be routed the exact same way so any "mechanical" failure will take them out together. Though the lock out requirement does add a few headaches on DLR network layout.
My customer wants me to set up their industrial computer hmi running factory talk view se client in the following way. They want to use a single...
1,034
Imagine, if you will, a series of custom built modules (building size). Each module is setup with standardized control/automation equipment...
5,631
Hi I want to connect 20 Delta PLC (DVP12SE11R) to an engineering system and read PLCs parameters in Citect Scada how can I do it? I dont have...
2,466
Quick question. If I install a Red Lion Graphite HMI w/ one of the digital input/output modules attached to an Ethernet/IP network with CLX PLC...
3,731
This question is about PLC Schneider Momentum M1 171 CCC IEC-960-30. We have one output element ADO 710 50 attached to the PLC via...
3,284