PLC Fault Routine in CompactLogix

Tweeker

Lifetime Supporting Member
Join Date
Nov 2007
Location
Smalltown
Posts
79
I am using a CompactLogix system and our customer wants to turn on two devices by default should the PLC fault. Can a Fault Routine turn on an output when the processor faults? How long will the output stay on if so?
 
Have the PLC output control a relay. In the PLC logic, keep the output on at all times. When the PLC stops, the output will turn off. Use a NC contact from the relay to energize the two devices you want to turn on. If the devices are anything more than simple indicator lights, make sure there is some way to turn them off regardless of the state of the PLC.
 
Steve Bailey has suggested a workable solution, but in answer to your post, it is not possible for CompactLogix to turn an output ON if the processor faults. If the processor faults, or communication with the controller is lost, then the output modules will turn all outputs OFF

ControlLogix output modules have the option to turn OFF, retain last state, or turn ON, for each output channel, but not CompactLogix output modules.

The given approach seems to be the best solution - hold some outputs true with an unconditional rung, and if the processor faults the relays will drop out. Use the n/c contacts on the relays to drive the "outputs" that must come on. When the processor restarts, the relays will be energised again, and the n/c contacts will open.
 
Steve Bailey has suggested a workable solution, but in answer to your post, it is not possible for CompactLogix to turn an output ON if the processor faults. If the processor faults, or communication with the controller is lost, then the output modules will turn all outputs OFF

ControlLogix output modules have the option to turn OFF, retain last state, or turn ON, for each output channel, but not CompactLogix output modules.

The given approach seems to be the best solution - hold some outputs true with an unconditional rung, and if the processor faults the relays will drop out. Use the n/c contacts on the relays to drive the "outputs" that must come on. When the processor restarts, the relays will be energised again, and the n/c contacts will open.

Actually, the 1769-L16 has the "output state in fault" option on its embedded I/O.
And, technically speaking, the 1769-L16 is a Compact Logix.
 
Actually, the 1769-L16 has the "output state in fault" option on its embedded I/O.
And, technically speaking, the 1769-L16 is a Compact Logix.

There's always one.... lol (or maybe more...)

Perhaps I should have said "If your chosen Logix5000 Output module allows it, you can ........."

đź““
 

Similar Topics

Hi, Experts: We have 20 + years old GE PLC series 90-30 stop running (the run led not on and battery led not on) and HMI showing that "PLC has...
Replies
7
Views
206
I'm working on troubleshooting a PLC for a piece of manufacturing equipment. The issue I'm trying to resolve is an open wire fault not getting...
Replies
2
Views
535
Hi I am biginner in B&R plc . Purifier system is transmitting the data to remote display unit. Currently there is no reading is display on remote...
Replies
0
Views
875
Hello guys. There is a fault on the PLC program that comes to the HMI panel via Data Block. This fault prevents the machine from working. Incoming...
Replies
1
Views
1,478
I need a little help figuring out how to fix a fault in a customer's CompactLogix. The guy said the fault happened when he was jogging the...
Replies
27
Views
5,335
Back
Top Bottom