Plx51-df1-eni in ignition

I've just installed on of these ProSoft devices in place of a 1761-NET-ENI. I got it to work on a MicroLogix 1500 by putting a 1,1 in the connection path using the MicroLogix driver.

The 1500 isn't really compatible with ignition so you need to check the don't browse processor under the advanced check box. In the designer you will have to manually enter the path for the tags like
Code:
 [PLC_Name]N7:0
 

Similar Topics

Hello, I have the PLX setup and configured. Its seen and downloaded to. However my ML1500 does not communicate over it. The port (0) is used...
Replies
5
Views
1,657
Guys, need help. How am I going to use this MSG instruction in RS Logix 500 to communicate in PLX51-df1-eni router. I already configured the...
Replies
4
Views
2,175
Hi. I am having trouble establishing comms between an slc5/04 and panel view plus 7 via a PLX51-net-eni. The set up is: 5/04 Channel 0 DF1...
Replies
8
Views
932
Good Evening , I'm looking for ways to log tags from a ControlLogix PLC. Have any of you used ProSoft PLX51-DL-232 Data Logger ? It...
Replies
0
Views
1,104
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
112