Point to Point Positioning with PF755
Jul 2007
Kiruna
600
I'm stumped with this. I'm attempting to perform some positioning using a Powerflex 755 series VFD. First time I've done something like this.
My first issue is homing. I cannot get it to work. By triggering the required bits in the HomingControl register I get the drive into homing mode and the motor runs as expected and hunts but doesn't do anything when the Homing input (wired to UFB card) on the drive is detected.
This homing I have been trying with the Feedback selected to open loop. This i only discovered tonight using the Drive Homing wizard. If change it to Port 5 Param FB1 Position which is where the encoder is attached then the motor starts to vibrate and nothing happens.
Anyone done this before? There are so many parameters in this drive and whilst I've used many times its a different beast in positioning mode.
Any tips appreciated.
I had this EXACT same issue a few years ago- but unfortunately cannot remember how I sorted it in the end.
If you are no better off in the new few days- I will dig out the logic and send across to you.
Oh that would be fantastic. I've spent days on this now with no success. I would be really grateful if you could share what you can. In particular the drive configuration.
@MorphuisOGrady :
This is and abstract of an application I found in my PC , It´s designed for an PF700:
Catalog Number:
1768-L4x, 1756-L6x, 1769-L3xE, PowerFlex 700 VC Drive
Title:
An AOI to convert movement of Virtual Axis in real movement over AC induction motors PowerFlex 700 VC driven, without any motion module.
Description:
This sample code shows how to utilize the AOI_PF700_VR_Axis
Product Family:
Programmable Controllers, Drives.
Product:
Control Logix, Compact Logix, PowerFlex 700 VC
Industries & Applications:
Automotive, Machine Builder-OEM , Converting, Material handling, Metal forming
Technologies & Functionalities :
AOI, Motion Control Routines, Ladder Logic
If you feel this can be useful, just let me know, send me an PM with your email.
I got the whole package.
@MorphuisOGrady :
Catalog Number:
Title:
Description:
Product Family:
Product:
Thanks for that. Do you have the application or a link to download?
@MorphuisOGrady : I have the software ( pdf explanation , XXX.acd, AOI etc) , I looked it up on Rockwell web page but did not find it.
It´s and old version, i have not tested , but just for the sake.
i have documentation that speaks of using a high resolution "absolute" encoder with the Powerflex 700s for "absolute point to point positioning"...
7,754
Hi, I have some problem with View Point which I'm using to manual control of conveyors. On begin when in network was only PLC and HMI View Point...
79
I have a bunch of tags in Historian/VantagePoint that off by one decimal point. I looked into the HMI displaying the same number, and the HMI is...
117
Good morning, I have a Emerson/GE PLC with Cimplicity SCADA. I need to export data of a specific point/object to a CSV file and load the CSV file...
287
Dear We are working in AB Studio 5000 and the drive is a PowerFlex 755T. For this project I need to control a conveyor to a certain set point...
149
