Positioning Application
Old No. 7
Jun 2010
Ohio
173
We have a project with a couple different fairly simple positioning tasks. Speeds are fairly slow and positioning doesn't need to be super accurate.
One is a mechanism raised and lowered by a ball screw and gearbox. The mechanism needs to be set to multiple positions. The second is a rotating table driven by a gearbox. The only position we need here is the "home" position so the loading mechanism can line up properly with the table.
A couple options we've looked at:
1. Servo - seems like overkill
2. PF527 w/ absolute encoder
3. PF525 w/ absolute encoder
4. PF525 w/ incremental encoder and home switch
#2 seems like maybe the best option, although the one we're least familiar with. Can/should the encoder be wired through the VFD? Or does it need to go to the PLC (Compactlogix)?
Any advantage to #3 or #4?
In each of those the encoder would be mounted to the motor tailshaft and wired to the VFD itself. Neither PowerFlex 520 series drive supports a load-mounted encoder.
The positioning in the PowerFlex 525 is basically dead reckoning: take how far you have to go, divide by the target speed, half that for the accel/decel stages = how long to run. Maybe the integral is a little more exact for S-curves, but that's the basic idea. Think of it as a "stop at target" instead of a positioner, which is fine for a very simple indexing table.
It's more sophisticated on the PowerFlex 527: it's truly a position axis in the Logix controller. You need at a minimum one of the CompactLogix with an "-M" part number for CIP Motion.
The first application challenge that comes to mind from your description is the vertical axis. Will there be a shaft or rail brake as well as a brake on the motor, to hold the vertical load ?
Rockwell has a decent application technique document about using Kinetix servo drives with vertical loads:
https://literature.rockwellautomation.com/idc/groups/literature/documents/at/motion-at003_-en-p.pdf
Torque proving for vertical loads is outside of the abilities of those PowerFlex 520-series drives. They just aren't made for crane/hoist applications like the 750-series are.
Thanks Ken. The vertical application isn't a hoist. Just a lift on a table raising 12" or so. The gearmotor would have a brake and I'm pretty sure the jack screws won't back out anyway.
"Positioning" may be overstating what we need a bit. I was initially thinking of just using the encoder more like a limit switch where we raise the lift until we get to x counts then stop. We're traveling at something on the order of 10 inches per minute and only need to get within maybe 1/8" of an inch. We've done some similar in a horizontal application where we just used an incremental encoder wired to the PLC with a PF525 set to coast to stop and a brake on the gearmotor.
I have a machine in design stage that has an AB Control Logix PLC, With 24 SEW Eurodrive VFD's.(Movidrive B). The VFD's are talking...
2,374
The system of position control is quite different in Beckhoff compared to Siemens. In a Beckhoff controller with Beckhoff drives on Ethercat, the...
855
I'm working on a SCADA project in FTView SE where there are many instruments, each of them has a Faceplate that can be called by a "Go-To Button"...
560
Hi, I am using P&F - WCS reader to read position of a trolley motion on a crane. Sometimes there is Ethernet communication failure error given by...
1,044
Hi, I'm stumped with this. I'm attempting to perform some positioning using a Powerflex 755 series VFD. First time I've done something like this...
3,519