Power Supply wiring of Modicon M340 BMX AMI 0810
TahirQ
May 2013
Riyadh
54
Can Anybody please tell me about the power supply wiring of Modicon M340 BMX AMI 0810 module. All i can get from the catalogues is Two wire sensor wiring.No info about power supply wiring.
the module itself is powered from the backplane. you must wire the sensors so that they provide the 0-20mA or -10 to + 10V signal to the terminals of the AMI module. How this analog circuit is powered will depend on the specific sensor.
I have done wiring of Digital I/O Modules only. This is the first time I am using an Analog Input Module.The Standard power supply module CPS 2000/2010 only powers up the module not the channels. I am getting confused because of wiring diagram of Analog Input Module as there is no explanation about how to power up the channels.
You Will Need an external dc supply to power your loops.
what i normally do is use 3 terminals per Channel
TERM1 - Positive 24vdc
TERM2 - Positive Signal
TERM3 - 0vdc coupled with negative signal.
then for loop powered instruments you connect to terminal 1 and 2 and for instruments with their own supply's you connect to terminal 2 and 3.
hope this helps
Without allowing for circuit breakers or fuses it should look something like this. Assuming you are measuring 4-20mA like chud mentioned.
Does Anybody how M340 interprets 4-20 mA current signal. In the form of Integers or Does it convert the current signal to BCD? I need this info for scaling analog input
Not sure but think its integers. But why do you need to know this? If you assign an integer to the channel you get int value. And scaling can be done on the cards configuration directly
I
Hi, does anyone know what a wiring diagram of a 240V power supply to a plc and pump looks like?
48
19,440
DaMan
D
I have the power supply in the link below. If we want a breaker to isolate and protect the input side how would I size that correctly being 120...
204
I am looking for power supply that I can mount on vertical DIN rail, and when mount that way is =< 4" wide. this is what I have now.... this is...
21
586
I have Rhino 120 to 24 dc power supply and it has 2 Positive and 2 negative terminals on the DC side but no ground terminal. Should I connect one...
439
We've still got a ton a PLC 5's installed and running. We lost a 1771-P7 Series B power supply. There are a lot of 1771-P7 series D power...
241