Powerflex 753 HeatsinkUnderTmp Fault
shawnhimself
Oct 2006
LBC
84
Like the title suggests. I have a powerflex 753 w safe-off board. I'm getting Fault 168 HeatsinkUnderTmp after a start command is given. The machine is in Peru...so not exactly freezing. I checked the temperature in the parameters and it's about 32C so again, not over the top either.
The drive ran fine for commissioning in the plant and about a day in CIP mode.
Occasionally I will get Fault 211 Safety Board Fault as well. o_O
Any help is HIGHLY appreciated.
Nothing in the rev notes.
It seems like the sensor is switching though. Sometimes it will run for up to 8-10 seconds before faulting, other times it will be immediately.
Has anyone replaced this sensor before? Is it possible to jumper this contact until a new sensor or drive arrives (could take 5 days down here).
Not sure how big this drive is but, if a wallmount, I'd ask for a warranty replacement. This kind of software irregularity can only lead to more mysterious nonsense later on.
At minimum, reload a current version of software.
@ The OP
DickDV has given you sound advice. You might try to upgrade to the next highest firmware rev but you are off to a bad start with this one. Drive replacement may be best.
I'm going to update the firmware in the morning and check out the sensor circuit. I'm also having a replacement drive shipped down...I'd just like to at least hobble my way through some production until then...I hope. Thanks guys.
This appears to be an environmental fault related issue, in most cases the drive is bad and must be replaced or call RA support for help.
Not 753s, I had 3 or 4 PF 200hp drives with bad temp sensors on the heat sinks a couple of years ago. After finally convincing RA, they had the local office replace a circuit board inside all of them.
Rockwell said its a bunk drive, ship it back.
Luckily I was able to source a similar drive locally in Lima. Back up and running(y)
How to remove faceplate from power flex 753 and not shutting the system down. What parameters should i change?
124
Hi all, I am having a problem with a powerflex 753 we have on site and keep getting input phase loss. The drive has been running for a long...
1,394
Hello Friends, We have a powerflex that stopped working sometime last week. It doesn't communicate over the network, or use CCW directly from my...
474
Hello all! I am fairly new to the world of PLC's and this forum, so I apologize for my lack of knowledge. I have a Powerflex 753 that keeps...
596
I am bench testing a PF753 (20f11nd096aa0nnnnn). I replaced the IGBT's and IC's in the firing circuit. Upon power up, I get the STS light...
754