Powerflex 753 not following Ethernet Commands.

HoldenC

Member
Join Date
Sep 2012
Location
Cumberland, KY
Posts
220
I have a Powerflex 753 that I can start with ethernet commands.

However, it doesn't follow the speed reference. It only runs at 60HZ.

Parameter 545 is set to Port 0-Port 4 Reference.

Can anyone offer any assistance ?


Thanks.
 
When it is running (at the incorrect speed), check parameter 935 (Drive Status 1) bits 10-14 to see what it is actually using as its speed reference.

SpeedRef.png
 
Does 592 also show 47.5?

Check you don't have a multiplier (549) or a minimum speed limit (522 for forward, 523 for reverse)

Running out of ideas here...
 