problem of communication
gamai
May 2011
meknes
hello
I have two SLC504 PV1000 communicating them to DH +
I tried to connect on the first SLC504 is not possible
with RSLINX I tried to configure the RS232 DF1 driver I could not
check cable message configures it impossible to connect
I made another test with RSLINX by configuring the driver 1747 -
PIC / AIC + driver I connect
Then in my browser I see my two RSWho SLC504 gold I could load a program and another there is a red cross on it
m can explain what is happening and I need to load
the program is on the second SLC504
thank you
Does the SLC5/04 you are trying to connect to already have a program in it?
If so do you have the offline file (it's .RSS file). Check the serial channels port configuration or post the file here and someone will take a look. ( zip the file first)
Was there anything connected to the serial port?
What cable are you using? It should be a null-modem cable.
Your screen shot shows Channel 0 set for DH485. If you have a real serial port on your laptop then use the 1747-PIC/AIC+ dirver. You must match the baud rate in RSLinx with your SLC's baud rate. You must have a different node address in RSLinx then your SLC.
Do you have a real serial port on your computer or are you using a USB to serial adapter?
Can you post a screen shot of channel zero's configuration?
See example below
yes I have a real serial port on my PC
his is the program I loaded the first SLC 5 / 04
I'm confused, are you trying to reconnect to the first SLC or are you trying to connect to the second SLC?
If trying to connect to the SLC shown in your picture above then configure RSLinx as shown below. If trying to connect to the second SLC, do you know how it's port is configured?
with this setup I connect on the first SLC5/04 but its DH + port and connect to the second SLC5/04 via its DH + port to connect to a port PV1000 via DH +
on the first SLC5/04 I managed to load the program
this is that it was possible to load the program from the second through the first SLC5/04 SLC5/04 by connecting to port 232
so I went on the second SLC5/04 with the same driver configuration to connect on port 232 I see that the communication is established and the led flashes but the 232 to load the program is not possible
Do you get an error message? Where do you see the communication? In RSlinx? Can you post a screen shot of RsLinx's RSWho?
I have an issue on my vessel, we have water tight door system created in China, company is no longer operating. We have 7 doors each with their...
174
Hello everyone, One of our machine we use Siemens Cpu315-2dp. And this cpu communicate with 4 Lenze servo drives series 9300 via profibus. Also...
198
I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
2,589
I am having PLC S7 200 smart model- ST 30 . In which I am getting problem in modbus communication of PLC and VFD via built in RS 485 port of PLC...
779
Hi, I have a Mitsubishi FX5U PLC where I cannot established communication via ethernet port of my computer. Search all videos and follow all the...
1,309