Page 19 just mentions "module location" under general specifications. That could be an error. Notice it doesnt mention the TB on that page, and yet the TB is the one that is mentioned everywhere else. Perhaps it's an issue with both the base and the firmware.
Here's another KB article:
70008 - 1734-IE4C base selection
Access Level: Everyone
Date Created: 07/20/2010 03:37 PM
Last Updated: 01/12/2013 01:34 AM
Where can I find 1734-IE4C (1734IE4C) base selection information?
Review the POINT I/O 4 Channel High Density Current Input Modules Installation Instructions Manual, pub. no. 1734-IN032A-EN-P - March 2008, starting on Page 5.
  • 1734-TB or 1734-TBS POINT I/O two-piece terminal base, which includes the 1734-RTB removable terminal block and 1734-MB mounting base.
  • 1734-TOP or 1734-TOPS POINT I/O one-piece terminal base.
On the other hand, since the IE4C doesn't have a 'unique' connection on pins 4,5 or 6,7, the TB3 should be OK according to another KB article:
59850 - 1734-IB8 and 1734-OW4 Point I/O modules compatibility with 1734-TB3 base
Date Created: 03/24/2009 10:20 AM
Last Updated: 07/29/2013 10:06 AM
Question
Are the 1734-IB8 or 1734-OW4 Point I/O modules compatible with the 1734-TB3 base?
Answer
No, The 1734-IB8, OB8 and OW4 are not compatible with the 1734-TB3 or TB3S bases.
  • Since the TB3/TB3S RTBs internally short the 4-5 and 6-7 connections together, any module that has unique signals on [4, 5] and [6, 7] should not used.
  • TB3/TB3S will short the Z to Z Ret, and Out 0 to Out 1 signals together.
Anyway, good luck. If it's not the firmware or base, I'm out of ideas :)
Since it's an L18, I am almost positive that is the issue. I'm looking at getting either a 3.2 or higher firmware or just getting an AENT. I really thought I was going nuts with this one.
Hi We're having issues with an FX1N-1DA-BD Analog output module. We're using an metallic contamination sensor MCS 1000 to detect particles. This...
117
Hi, I tried today to get RD3A and WR3A instructions to work on the PLC and it didn't work, but it worked in simulation. I followed the clone...
18
1,446
Hi, Sorry for my bad english, I'm from Poland. I've decided to learn basic PLC programming as hobby and to maybe get a better job. I have...
1,342
Good evening, just a dump question, I’ve configured channel no 13 with scalling as attached, then shown not linear reading, even when i simulate...
1,713
I have a SLC5/05 with a 1746-NI16V. I am trying to configure it for single ended inputs. Please notice in the screenshot the upper SCP is...
21
5,533