I'm working on a project that will be using the Schneider TeSys starter with a Profibus interface. There is a power tap module that is used to add 24VDC power along with the Profibus cable.
Is there such thing as a 4 wire Profibus cable? I can't seem to find any. This documents appears to show 4 wires in one cable:
http://www.global-download.schneide...E83878825757800494023/$File/1639560_01a55.pdf
Page 2 of this document shows the power tap module (LU9GC7) with a single cable coming out:
http://www.global-download.schneide...6D14188257578005F546C/$File/1639544_01a55.pdf
In the lower left corner of your first document, it shows the stripping specs. for the cable. In that box, it lists the part number as LU9RPB***. I'm guessing that's the Schneider part number for this 4-conductor cable? The *** is probably for the length, Maybe your Schneider rep. can recommend a Belden equivalent?
-Eric
Eric
I noticed that number in one of the other documents and tried to Google it with no luck. But when I tried LU9RPB100 it turns up a lot of results. It is a schneider cable part number.
I'll check with the rep to see if they sell it in bulk or have an equivalent in another brand.
Archie
Archie,
I have worked on projects where customers have used DeviceNet cable in place of ProfibusDP cable because they wanted Power & Comms to be on the same cable. They weren't running 12Mb, but at speeds of 250Kbps or slower it seemed to work fine.
Joe_WaZoo
Interesting idea to use DeviceNet cable. I'm sure as long as the length is reasonably short and the speed slow enough, there would be no issues.
What I have found is that Belden 9184 (2 twisted pair) cable has the same impedance as Profibus cable and a capacitance within the range of Profibus designated cables.
Hi Folks, I am new to the S7-300 and the whole Profibus communication. And I just wonder that can you connect a S7-300 module to a Beckhoff Bus...
322
Hello everyone, friends. We have a machine where our main CPU is a Siemens S7-300, but with different makes and models of drivers, and modules...
18
3,781
Ok here is the problem we have a Siemens DP PLC (Master) and RIO ( slave) at the end of a Fiber Cable that runs through a Slip ring via OLMs...
493
Hello guys, I need your help regarding the proper termination of Profibus cables. I now that in theory in order to minimize the noise and to...
3,641
Dear All, I want to know, due to aging, temperature and humidity present in the room, the power cables got hard. This hardening does effect the...
1,641