Profibus Communication problem for 200m
engrselva
Dec 2007
singapore
23
Hi Guys
I have connected 2 s300-314C-DP plc in Profibus. as I am running in test mode, I noticed both can communicate only in lowest bus speed. For the testing, the bus lenght is only 15m. But, in actual project, it is going to be 200m. I am worried, it miht be a problem in communication in real situation. can any one help me. what causes this problem?
regards
selva
Thanks for your reply. but, I heard the PROFIBUS can support upto 1000m!!. That why i am in confussion. Is there anything wrong in my programm setting, configuration....?
Thanks in advance.
regards
selva
The lower the bus speed, the longer the distance. Though you should be able to communicate at higher speeds in you test rig, check your network configuration.
Maximum 50m without repeaters according to Siemens. But I have a installation with a 300-350m cable without any repater, with low speed it works perfectly.
It depends on the bus speed, at 12Mbs then 50m but at 9600kbs it is 1000m
Dear All, I have a KUKA Palletizer machines having Iconics Genesis SCADA installed on its PC. It remained closed for about 7 to 8 years. We are...
963
Hello guys, I have problems with the Porfibus communication to my regulator Siemens Sipart DR 21and my PLC rockwell 1756-L161. So, for the...
2,103
Hello to all, I have a strange problem with establishing the communication between WinCC HMI station and the rest of Profibus network. We have...
3,872
We are having Siemens s7-400 dcs system, we are using profibus dp communication for dcs & all ABB vfd drives (ACS800). Now we are facing major...
3,173
Hi everybody, An IPC connected to a Siemens PLC as a slave module. When I restart the PLC while IPC running then PLC can't find the IPC node on...
9,150