Pump Control with a PLC
It looks like you've been given a lot of leeway so you first have to decide what you are actually trying to control. Based on my reading of your spec most likely you're trying to maintain a tank level. If one pump can't do the job, you start the second. If that's still not enough capacity you add the third, etc. Similarly, when the number of pumps is more than the demand calls for, you shut them down in sequence.
First, answer some basic questions. Is the pump motor going to be controlled by a starter or a variable speed drive?
Depending on your choice, what are you going to need for PLC outputs?
What are you going to use to sense that a pump is running?
What other sensors are you going to need based on your choice of control strategy?
Once you have selected a control strategy, figure out how to get a single pump running and controlling the system. Once you have that working, duplicate the logic for a second pump. Then figure out how you will detect when the one pump isn't getting the job done and how you can use that information to start the second pump.
The overall task can look overwhelming, so break it into smaller pieces that aren't as complex.
good night friend, would you charge how much to translate a clp programming from onron (cx one) to simatic 7 (tia portal v15 from siemens?
there are 17 pages with two columns of ladder programming in cx-one.grato
50 USD per rung, 50 USD per branch, plus you need to buy cx-one and tia portal v15 for me to keep.
I'll do it for half the rate of this guy. Never worked with either package before, but how hard could it be? And the client doesn't really check anything is working properly at the end, so....
- A number of my competitors
I'm looking for a solution to a problem we are having in our water treatment system. We add a lime slurry to the water prior to it going through...
29
11,001
hello, i am a entry level student studying plcs. i was wondering if anyone could help me with a problem. i need to control 2 pumps. using a...
3,640
P
My problem is that i want to control water level in a over head tank using a plc .that means to switch off the pump when the tank fills and to...
8,162
Hi everyone, I am a newbie and I have trouble in the control sequence. I have a system with 4 pumps. The required: Ex: Push a button to start in...
21
2,767
Hi there, We have a system at a water treatment plant where large raw water tanks feed into the plant that's all on the same level. At high tank...
18
3,769