Question regarding Cat 4 safety circuit
Short Circuit
Jun 2013
Ohio
I have three VFD motor drives. One is 480VAC from a set of fuses and a power distribution block, another is from a different fuse / distribution block supply, and the third gets its power from a 480 to 400 volt step-down transformer.
My questions is: in order to make it pass Cat 4 safety do I need two contactors in series to interrupt the power to the VFDs during an E-Stop press? That would make buying six contactors.
I have read some comments if it is better to interrupt the line or load side of the VFD but that is not my question. I am just wondering if I need two contactors per VFD.
Thank you
Yes, sounds like you will need two safety contactors in series per drive.
Depending on the supply wiring configuration it may be possible to have two safety contactors killing the supply to multiple drives while still meeting Cat 4 requirements but from your description doesn't sound like it's feasible.
In my experience it's better to kill the line/supply rather than the load.
I know this can be done, but I can't get the router config right. My goal is to physically connect(using an ethernet cable) a device(PLC, RTU...
1,028
I haven't had to tune a PID loop in a very long time. It's actually a PI loop for a pulse width modulation s.v. What was the name of that tuning...
4,122
Hello, I have a question regarding the analog output modules on a AB Micro850. I'm not getting an output to my valve and when I put a meter on it...
1,540
Happy new year everyone. This is more of a Electrical engineering question than a PLC one. Can a Motor and a VFD that is rated for 240/480...
29
9,992
This may be a simple question. I understand the concept and application of analog modules (i.e. Compactlogix) for transducers, and outputs for VFD...
2,102