Quick question: Discrete IO does not need Block Transfer

All discussion above is for 1771 ASB and modules

With 1794ASB it is a little different.
First what series 1794ASB you have? This is very important.
Only series E supports 32 points modules and has different DIP switch settings tham all other modules.
First get the User Manual;
Ser E: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1794-um009_-en-p.pdf
Older Modules: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1794-um003_-en-p.pdf

With any 1794ASB adapter supports up to 8 physical modules.
With 32 pt modules and ASB/E you can use 32 bit addressing and this will take up to 2 logocal racks. See examples in the first manual.
 
Contr_Conn said:
All discussion above is for 1771 ASB and modules

With 1794ASB it is a little different.
First what series 1794ASB you have? This is very important.
Only series E supports 32 points modules and has different DIP switch settings tham all other modules.
First get the User Manual;
Ser E: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1794-um009_-en-p.pdf
Older Modules: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1794-um003_-en-p.pdf

With any 1794ASB adapter supports up to 8 physical modules.
With 32 pt modules and ASB/E you can use 32 bit addressing and this will take up to 2 logocal racks. See examples in the first manual.

Thx for ur info, so with this settings difference, I assume ASB older than series E does not support 32 pts base, right?
 
ckchew666 said:
Thx for ur info, so with this settings difference, I assume ASB older than series E does not support 32 pts base, right?
As far as I remember this statement is correct, only ser E supports 32 pt modules.
It has different DIP switch settings compare to older modules.
 

Similar Topics

So the quick and short of the situation is that I designed an axle press that was sent to one of my company's other facilities. That facility just...
Replies
19
Views
4,250
So I have a PID loop on an 1756-L61 running V17 software just for background. Also the PID PV is a pressure transmitter and the CV is speed sent...
Replies
1
Views
895
Has anyone come across a 3 turn potentiometer that is panal mounted with either a 22 or 30 mm hole? I have been looking but nothing so far. They...
Replies
20
Views
4,718
Hi, I am just learning CCW, finally got connected to a micro820. I'm wondering what the Version number means. The program that was already in the...
Replies
1
Views
1,624
How do I measure if I am getting a signal out of the plc output? All of the outputs are giving me the same voltage, however I am certain that not...
Replies
6
Views
2,169
Back
Top Bottom