Quick question on OMRON CPM1A
ckchew666
Aug 2003
Malaysia
591
Anybody know if CPM1A 10 points module can add expansion module?
Or only certain model support expansion (MAD01)?
I'm looking for 1AI and 1AO OMRON plc.
Thanks.
The CPM1A-10 and CPM1A-20 units are NOT expandable. You must use a -30 or -40 to have expansion capability. All CPM2A cpu's can be expanded.
The CPM1A-MAD01 has two analog inputs and one analog output. Be careful, this unit only offers 8 bit resolution (0-255 decimal). The CPM1A-MAD11, also two analog in and one analog output offers 0-6000 decimal resolution.
Hope this helps.
Hope this helps.
Thx for ur info. I do not know such limitation exists.
0-255 means when I inject 4mA it'll shows 0 and when I inject 20mA the max. it'll show 255 only? If yes, then the resolution is very low. Am I right?
You are correct. This is a rather low resolution analog unit. The actual values will be in hex 0-FF (0-255 decimal). If you need more resolution, the CPM1A-MAD11 should do the trick.
Any other questions, just ask.
Thx for ur help...u r good in OMron :)
gtsuport: Sorry to trouble you again, looking at the cheaper model between OMRON (ZEN) & AB(PICO), what is the limitation with ZEN? Does ZEN has any analog OUTPUT (1 at least)?
PICO has built in 4 AI & 1AO. I'm soucring for the price from Rockwell.
Anyone know if the CPM1A-40CDR-D-V1 comes with any AC input? Becauses all the field devices are running on 110AC (push button, sensors...)
Thanks.
24VDC inputs only.
Have a look at the Mitsubishi Alpha 2. It has AC inputs and analogues. Similar in size to the ZEN.
Im trying to do a simple program on an Omron CPM1A unit. The problem I've got is using the pots on the front. It says in the manual that it the...
3,198
So the quick and short of the situation is that I designed an axle press that was sent to one of my company's other facilities. That facility just...
19
4,305
So I have a PID loop on an 1756-L61 running V17 software just for background. Also the PID PV is a pressure transmitter and the CV is speed sent...
915
Has anyone come across a 3 turn potentiometer that is panal mounted with either a 22 or 30 mm hole? I have been looking but nothing so far. They...
20
4,781
Hi, I am just learning CCW, finally got connected to a micro820. I'm wondering what the Version number means. The program that was already in the...
1,638