Random Numbers
Guest
Guest
G
I have a DL340 which takes the 4-20 ma signal from WI127( Scale) analoge bioard.when scale shows 0 Kg -PLC shows high random numbers when I monitor that register with HHD.This is not happening when there is something in the silo.IS something wrong with the analoge module ?
Sounds more like the scale is not calibrated with the analog board and is sending less than 4ma. When this occurs if you are scaling to engineering units, you will be outside of your range and then "wrapping" around. Check the zero point of your scale and then put a 4-20ma transmitter on your analog card and check the zero point of the card. The reading should match. If not, then you will have to correct it by changing the sclae zero point or go into the programming and change it there.
I changed the AI modual and calibrate the scale for 4-20 ma but still is the same.
I am thinking that noise can cause this issue .or the Analouge board inside the scale sending this .
any ideas?
Yes, but did you check the signal for the zero point of the scale against the zero point of the card?
4 ma is not alsways 4 ma. It should be, but rarely are two pieces of equipment calibrated the same "out of the box." Even equipment that is supposedly calibrated to ANSI or ISO standards may not read the same when it is installed in the field.
I suppose that it could be noise, but you state that:
This leads me to believe that the zero points of the two devices do not match...
Hi there, Has anyone ever had to generate random numbers for an application? I can do this with an algorithim using the RTC as a seed but what...
10,759
Does anyone have any representative code they're willing to share that will will generate some random numbers? I'm playing around with...
12,673
Hello Everybody, We have an DL340 cpu whcih inputs 4-20 ma signal from scales to show the weights. Now this value needs to be subtracted from a...
1,695
Y
I have been trying to make a random number generator using RSLogix 5 and 500 but can seem to get it completely random. I have tried using...
7,149
Looking for some advice for backing up the programs on a bunch of old random PLCs. All I'm really concerned about is getting the program out of...
43
4,722