Read GV3000 Drive Status with RSLogix5000 over Controlnet

WebRanger

Member
Join Date
Apr 2006
Location
Portage, Indiana
Posts
18
I need to read Drive status from 10 GV3000/SE drives. I am using ControlLogix processor @ V13.31 and the path is via ControlNet. I see plenty on MSG examples to perform various reads but nothing yet on how to configure the MSG Control Block for these devices.

Any comments will be appreciated?

Speaking of GC3000/SE drives on a ControlNet, I am also experiencing very intermittent NCL errors on my drives but RSLinx shows no errors occuring and the Station Diags for all the nodes contain zeros in the error entries. 5 of 10 drives fail, always the same 5 and at exactly the same instant?

Any diagnostic suggestions?
 
Last edited:
Gv3000

I can't answer your question, but was just checking in for some info on the GV3000. I have a single drive that is giving me a HU fault (High DC voltage) I was looking to see if there is a way to install a braking resistor.
 
WebRanger said:
I need to read Drive status from 10 GV3000/SE drives. I am using ControlLogix processor @ V13.31 and the path is via ControlNet. I see plenty on MSG examples to perform various reads but nothing yet on how to configure the MSG Control Block for these devices.

I have only done this from a PLC5, so I will have to defer on the details of the control block for controllogix.

WebRanger said:
I am also experiencing very intermittent NCL errors on my drives but RSLinx shows no errors occuring and the Station Diags for all the nodes contain zeros in the error entries. 5 of 10 drives fail, always the same 5 and at exactly the same instant?

Any diagnostic suggestions?

Your errors would appear in the controlnet status words in the PLC processor...not necessarily visible on RSlinx (or did you mean RSNetworx?)

NCL errors on a single drive, in my experience were usually caused by a failing comm card in the drive (especially with the bookshelf style European drives). Having multiple drives fail at the same time tends to incriminate the cabling, taps, or any repeaters that you may have.
 

Similar Topics

Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
Replies
4
Views
152
Is there a way to use the FAL instruction to do +=2 instead of +=1? I have an array that is organized with alternating "data" and "flag" values...
Replies
5
Views
126
Hi everyone i have a customer, who wants to show an alarm on the machine, if the I/O forces are enabled and set, on at ControlLogix L81E with...
Replies
3
Views
254
Hi Iam using monitouch hmi(V9 soft) with omron plc cj2m (CX programmer). In this I want to read a data from hmi to plc. The data was like...
Replies
0
Views
101
Hi everyone. Quick questions. On UnityPro, I want to open and quickly read tags from a .STA files witouth opening the program. I have 30 plc...
Replies
2
Views
149
Back
Top Bottom