Recommanded Asolute Encoder Brand.
I've used profinet/profibus versions from this company for years. Reliable and not too pricey.
https://www.kuebler.com/en/products/measurement/encoders
If the encoder is being used to calculate a speed as well as position, the update rate should be synchronous to what ever is calculating the speed. Profibus is pretty fast but it isn't normally synchronous. However, sometimes it doesn't affect the application much.
I've used Sick encoders and Allen-Bradley Ethernet/IP encoders with good results. Hard to wrong with either brand really.
Any of you would recommend a brand for absolute encoder on a drive shaft.
This is a pretty ambiguous request.
First, do you mean single turn absolute or multiturn absolute? These are different beasts.
What will you be connecting the encoder to? What types of signals does it accept? SSI is mentioned a lot in this thread so far. Also Bus networks are possibilities as well as BiSS and EnDAt. Here's an article comparing some of these:
https://www.motioncontroltips.com/a...differences-between-ssi-biss-hiperface-endat/
Do you need to reach a certain resolution counts / revolution?
What is the environment like where the encoder will be installed?
What is the form factor required for the encoder; shaft output? hollow shaft, cable out the back, cable out the side, etc...
Sick has plenty of options. So does Danaher.
Dynapar is OK too.
I just said Sick as my first choice because I/we have been working with them the longest. Back in the late 1990s a person from Stegmann posted on sci.engr.control about the new Stegmann SSI encoders. I was interested because for that there was only resolvers. I didn't like resolvers because every company had their own standards and the resolvers didn't respond well to fast accelerations. I/we jumped on the Stegmann resolvers. The SSI standard is now fairly standard. There are still some companies that mess things up by adding extra bits at the end. Sick ended up acquiring Stegmann.
What will you be connecting the encoder to? Connecting to Drive
What types of signals does it accept?SSI
Do you need to reach a certain resolution counts / revolution? more the 1024 is fine
What is the environment like where the encoder will be installed? wet and dust environment
hollow shaft
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
242
I have an application using an incremental encoder and then I convert it to degree (0-360) using calculation program. For a while, the calculation...
328
Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
18
1,045
Dears, i am trying to change the series of encoder from A to B, but the program do not has this option (Rslogix5000, 20.06 the old encoder was...
216
Hi all, I am working with an incremental encoder (ABZ signals, 360 ppr (so 1440 counts per rev)) to replace the existing "manual" encoder wheel I...
51
2,639