Now, just to add fuel to the fire, are we talking conventional current or electron current? LOL
I have found on solenoids that need a rapid off, therefore CANNOT have a flyback diode on them, I use 2 or 3 poles of the interposing relay wired in series. This provides 2 to 3 times the air gap helping quench the arc associated with the collasping field in the solenoid. The current is interrupted faster and you have NO current in the windings and the solenoid drops out the fastest.
ALWAYS use interposing relays between a PLC and a solenoid or motor starter coil. The relay takes 30 to 45 seconds to replace and you or some maintenance person will be replacing it at some point in time.
Coils are a dead short to current when voltage is first applied. the magnetic field that is built up around the windings develops the CEMF that sets the holding current. AC has less issues than DC but both fry relay contacts DC just faster than AC. Some DC contactor assemblies have an internal resistor that is switch in series with the coil after the contactor closes to limit holding current and extend the life of the coil.
I have measured as high as 500 volts DC kick on some 120 volt coils when the power is removed. I have found using 1kv prv diodes last the longest. 1N4007, 1N5551 if you can find them, seem to last the longest. If you have high cyclic rates on the coils, a full wave bridge rated at 1KV 20a holds up even better.
My $00.02 on the subject.
I have found on solenoids that need a rapid off, therefore CANNOT have a flyback diode on them, I use 2 or 3 poles of the interposing relay wired in series. This provides 2 to 3 times the air gap helping quench the arc associated with the collasping field in the solenoid. The current is interrupted faster and you have NO current in the windings and the solenoid drops out the fastest.
ALWAYS use interposing relays between a PLC and a solenoid or motor starter coil. The relay takes 30 to 45 seconds to replace and you or some maintenance person will be replacing it at some point in time.
Coils are a dead short to current when voltage is first applied. the magnetic field that is built up around the windings develops the CEMF that sets the holding current. AC has less issues than DC but both fry relay contacts DC just faster than AC. Some DC contactor assemblies have an internal resistor that is switch in series with the coil after the contactor closes to limit holding current and extend the life of the coil.
I have measured as high as 500 volts DC kick on some 120 volt coils when the power is removed. I have found using 1kv prv diodes last the longest. 1N4007, 1N5551 if you can find them, seem to last the longest. If you have high cyclic rates on the coils, a full wave bridge rated at 1KV 20a holds up even better.
My $00.02 on the subject.