I'm still unsure of what the "device id" should be in Crimson under the device config in the BACnet master driver. I spent a little time on it yesterday and still was unable to communicate. Also starting to wonder if the pinout is right. RL tech support instructed me to use pin 1 -, pin 2 +, and pin 6 common.
This is RS232 basic. Pin 1 and Pin 2 are read and transmit not Plus/minus Pin 6 is common. Depending on the wiring on the field unit you may need to switch Pin1 and Pin 2. On your field device you should see Tx and RX or something of that nature Tx is the transmit line and Rx is the receive line. The receive line on your device (chiller, whatever) connects to the Tx on your G3. Since you use AB you do this without noticing by using a null modem (well actually the null modeme does a bit more but that part is not needed for this discussion).
Anyway the point is when trying your diffent comm settings try switching just the RX and TX and leave the Common alone.
Part of the problem may be the fact that the chiller in not a slave....I'm just treating it as one. According to Johnson Controls there is no way to set this particular unit up as a true slave.
Sorry to say I have no direct experience with BACNET but on most other Comm systems if it can be a master it can be a slave. The only thing that would prevent it from being a slave would that you could not address it. Not real sure what a "true" slave would be. Either it can be addressed or it can't.
Anyway this is a side issue.
From the manual posted I see you have read only and write only and read/writes.
Start with the Reads. Do not mess with the Writes yet. Set your reads up on your screen along with your Comm error word you can create in the G3 (refer to the Crimson Manual for more details).
Now you can play with the comms settings and wiring and find out when you actually have it working. Your Comm Erros should go to zero and you should see new data in your words. This will also let you know if byte swapping is taking place.
Remember a Write only works when the data changes, otherwise it just sits there so get the reads first. Once you have the reads working then your comms work. Now comes the fun part of getting the writes to work without clogging the system. That is where you get into timing.
Also that Comm Error I talked about earlier. It comes in real handy during this phase. Well it does in Modbus I can say for sure.