RSNetwork for DN Point IO
eight_bools
Apr 2019
Oklahoma
71
Hey guys
Im thinking about using some point IO on and old SLC 5/05 with a device net scanner.
I have RS Networx and have looked at some other scanners that we have on other machines to see how it works. I was able to add the 1734-ADN but do not see how to add the IO modules to the IO adapter. I can add the IO modules but they show up with a different node address.
Anyone have any pointers on what I am missing.
POINT I/O with DeviceNet was a weirdly flexible product. The backplane of POINT I/O is really just DeviceNet at 1MB.
When you used a 1734-PDN, the DeviceNet network basically passed the packets straight through to the connected modules. They all took up a whole DeviceNet node number of their own, and you would see them individually on the RSNetworx project.
The 1734-ADN is a different animal: it is itself a Scanner on the POINTBus side, and an Adapter on the DeviceNet side.
So you actually need two different RSNetworx files: one to map the POINT modules into the -ADN's Scanner side, and another to map the -ADN's assembled I/O image into the Scanner from an PLC/SLC/Logix.
You would almost expect to be able to double-click on that 1734-ADN and open up another instance of RSNetworx or an applet to configure it, wouldn't you ? But you dont: you create an all-new project file with the 1734-ADN as a Scanner.
It's clunky at best, which is one reason it's been almost entirely supplanted by the 1734-AENT and EtherNet/IP.
But it does work !
I built a system with what could be best described as "failover" I/O where a ControlLogix Redundancy system ran remote chassis on ControlNet each of which had a 1756-DNB that scanned some special sensors as well as several 1734-ADN adapters. Each ordinary discrete or analog sensor was wired to two separate POINT I/O modules.
So I needed two *.DNT files for the two 1756 Scanners, and a total of six *.DNT files for the 1734-ADN adapters, four of which were identical except for their serial numbers.
Let's just say that when I came back to it after six years I was grateful for 2010-me writing good notes.
Hi, I have some problem with View Point which I'm using to manual control of conveyors. On begin when in network was only PLC and HMI View Point...
80
I have a bunch of tags in Historian/VantagePoint that off by one decimal point. I looked into the HMI displaying the same number, and the HMI is...
120
Good morning, I have a Emerson/GE PLC with Cimplicity SCADA. I need to export data of a specific point/object to a CSV file and load the CSV file...
290
Dear We are working in AB Studio 5000 and the drive is a PowerFlex 755T. For this project I need to control a conveyor to a certain set point...
149
Hello colleagues Anybody knows, what could be the best or a better option to bring with you when you are in service at factory to connect via...
270