RTD > 4-20mA connection to AD041
davidelh
Sep 2013
malaysia
hi guys.
im new to analog system. ive been doing a temperature reading from a sugar tank.
I have made connection frm the RTD to a 4-20mA converter. But the question now is how im going to connect the 4-20mA (+) and (-) wire to the OMRON AD041 extension unit?
The (-) should connect to COM and (+) should connect to IN1 right? Any thing else that i missed?
I saw some application that connect 24V to the IN1. This is confusing
Generally the wiring is power supply plus to transmitter plus, transmitter - to I/O card +, I/O - to power supply -.
This is, I know, a silly question, but have you looked at the Omron manual?
Depends.
Depends on whether the transmitter is 2 wire or 3 wire.
Depends on whether the AI can power the loop (most don't, most require separate power supply connection).
Like Tom says, what's the manual tell you?
set the voltage/current switch to current.
connect the a2 to gnd
connect the output or - from sensor to A1
connect the input or + to 24 volt.
Good day all, I am having bit of an issue getting my head around this RTD scaling issue. Be forewarned, my head has been known to be "THE" issue...
24
8,853
Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
1,205
Good Afternoon , It seems like we always have problems with using Type J Thermocouples with our slip rings . Would using a RTD at 10...
1,650
We are running a power flex 70 connected to a Delta V and I cannot get the drive to start because I am getting a STOP ASSERTD message on my HMI. I...
3,078
I am working on an installation that will require sensor cabling interconnecting sensors to PLC subject to outdoor temperatures. Will the ambient...
2,066