RTD input card (1769-IR6)

adamp

Member
Join Date
Mar 2013
Location
newfoundland
Posts
12
Hello, im using a mircologix 1500 plc with a 1769-IR6 rtd input card. I am having trouble getting the readings from the rtds to displays as values in rslogix 500. Any feedback or information on this would be greatly appricated. Thanks!
 
Welcome to the Forum!

What Scaling Type have you selected in the IR6 Card?

What form do you want the Values to display in?

Stu.....
 
Thanks for the reply.
Ive selected raw/proportional for the data format and upscale for an open circuit condition. Which is the value currently being displayed on the screen. Im not sure which scaling type i have selected. My main problem is getting any value from the rtd to display in a MOV having source as I:3.0 and dest as N7:1. Once i can get a value to display within this function i think ill be able to figure out the scaling.
 
Post your .rss file, zip it first.

Are you getting any reading at all, if so what?

What type of RTD (PT100 or ???)? 2 wire ,3 wire, 4 wire?
 
My main problem is getting any value from the rtd to display in a MOV having source as I:3.0 and dest as N7:1.

is the Source of the MOV command changing - but the Destination doesn't? ...

if the MOV command is in a "new" subroutine (ladder) file, make sure that you've included a JSR (Jump to Subroutine) instruction on an unconditional rung back in Ladder File #2 ...
 
When I check across the exc and sense inputs on the card im reading 108 ohms which is about the right reading at room temp. I think my problem is I:3.15 will not stay at 1 which enables the channel.
 
No, the source and destination value are the same. Which is the upscale value of 32767. Also there is a JSR in place. I have even tried bringing in the value on lad 2 with no luck
 
When I check across the exc and sense inputs on the card im reading 108 ohms which is about the right reading at room temp. I think my problem is I:3.15 will not stay at 1 which enables the channel.

I:3.CH#/15 is part of the Measured Value, not the Enable Bit. The IR6 Card Setup is done in the I/O Configuration for the ML1500.

Can you Post your PLC Program? (Zip it first)

Stu....
 

Similar Topics

Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
Replies
4
Views
1,205
I had a question with regards to an Non-Isolated vs Isolated RTD Input Card. This would be for a Flex 1794-IR8 vs Spectrum (1794sc-IF8U or...
Replies
1
Views
1,792
Hello all. Is it possible to run an RTD to an Compactlogix Analog input module, without any sort of a signal conditioner or anything like that? Thanks
Replies
4
Views
2,216
Hello guys, did you ever measure the voltage on RTD PT100 probe connected to the analog input card? Since temperature is measured with three wire...
Replies
5
Views
1,480
hi . we are using beckhoff decentralised I/O module on profibus , which has its different analog cards for RTD , current and Voltage input. i need...
Replies
12
Views
5,913
Back
Top Bottom