S7-315 to Honeywell PGM
adfox
Jun 2006
Poland
334
Hi, I'm facing some hardware selection problem for S7.
I have a Honeywell system that will communicate with my S7-315-2 PN/DP.
S7 will have 10 profibus slaves on 1 DP network and will be a DP slave for Honeywell using S8 profibus gateway module.
As S7 cannot be master and slave at the same time, i have to select a CP, and there is a problem:
CP-342-5 can send/receive max 240 Bytes in slave mode and I need a little more (circ. 300-360).
I was thinking about DP/DP coupler - but again it can only handle 240 bytes.
What do I need on S7 side to send more ( and I cannot multiplex send data ) ?
Here's the Honeywell PGM:
https://www.honeywellprocess.com/library/support/Public/Documents/Profibus_Gateway_Module_User's_Guide_EXDOC-XX88-en-110.pdf
How time critical is your data?
You can send different data if you want, for example, use the first INT as an identifier 1 or 2.
Then on the other end of the line they look at the identifier and put the data in place accordingly.
You might be able to do generic send/recv commands (FMS or FDL) instead of Profibus, to send more data. This would probably be less deterministic, but might allow for more data. I'm not sure what is supported on the honeywell side.
As far as I know, 244 bytes of IO data is a Profibus limitation. If you want to send the data via Profibus, you would need to split the data somehow. You said you can't multiplex the data, but maybe you could use two slaves to transmit the data. This could either be 2 CP cards, 2 DP/DP couplers, etc. Technically, it could be one of each as well, but that starts getting messy.
Data is rather critical - simocode data from switchgear / commands from DCS - I'll go with 2 CPs - Thank You.
Hi All, As a precaution my company has been collecting copies all the HMI and PLC programs. I have recorded copies of most of our sites...
76
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
183
Hi , Looking for some help. We have a 343-1 PN Lean Card & 315-2DP connected to an external system collecting data. After a recent shutdown...
71
Got a VIPA 315-2AG23 that i try to go online with but can't seem to make it work through a network. I can go online if i'm plugged directly in the...
283
I'll preface this by saying this is the first time I've worked on a Siemens system and I'm fairly unfamiliar with them. I might mess up some of...
29
801