S7 DP/DP Coupler. Is 1st bit a "OK" status bit ?

JesperMP

Lifetime Supporting Member + Moderator
Join Date
Feb 2003
Location
ᚴᚬᛒᛅᚾᚼᚬᚠᚾ
Posts
16,342
Maybe this is obvious to someone more experienced with DP/DP couplers than I am.

We have setup a system with my PLC connected to a supervisory PLC via a DP/DP coupler.
Notice that there are OLM copper-to-fiber converters in between the two Profibus networks.

What puzzles me is that the very first input bit in both directions is always on. It cannot be controlled by the corresponding output bit in either of the PLC's.
For example, my inputs start at I40.0 and this bit is always on.
Is this normal ?
Is it kind of a status display that the connection is OK ?

Everything else works as expected.
One thing is that I have set the DP/DP Coupler to be "fail-safe", i.e. Inputs goes off if the connection is lost.
 
Ah, how I could have overlooked this in the manual I dont know.

It says clearly in the manual that if the DIA switch is on, then the 1st input bit behaves as I have observed.
 
Hi! Indeed, that is reserved for a DIAGNOSIS and data comparison between the 2 networks. I dont remember if a 0 is for data missmatch or a 1. If you are trying to send words or bytes in the first byte, try to set 1 byte spare in the first input asociated in each dp network and then continue with your I/O definitions

Greetings
 

Similar Topics

Afternoon all, So, i have an output that is being fired from 2 inputs separately. 1st input is a sensor, when something passes by it should...
Replies
0
Views
326
Hello all! I have a PN Coupler connecting two PLCs, one on X1 and one on X2 and am able to transfer data using the IN and OUT configuration...
Replies
1
Views
1,193
Dear experts i have an installation running with S7-1515 and a quite huge profinet network. i encounter an issue with a Siemens PNPN coupler...
Replies
2
Views
2,184
For connecting to a Micrologix through a 1761-NET-AIC, the manual specifies that you should use "RS 232 Communication Cables Cable, Cat. No...
Replies
0
Views
1,376
Hi. I'm struggling with configuration of PN-PN coupler 6ES7 158-3AD10-0XA0. The situation is as follows: I have 1 S7-300 PLC on the X2 part of...
Replies
13
Views
5,064
Back
Top Bottom