S7 hardware probs
kevbloke
Jul 2004
Kent uk
81
Good morning guys,
I have a 315 cpu which is running but with a fault which im not sure what to do about. Im after some input please.
When i go into hardware diagnostics its telling me that it has no communication with node 5. There is no node 5. There may have been once and been removed but there isn't one now.
If i go into the hardware configuration there are several other nodes shown. The strange thing is that this machine (a plastic labeller for pet bottles) is actually still running so its only an issue in as much as i would like to know how to loose the warning lights.
Any ideas please
Kev
First of all what "fault" you are facing? what is the Node address, which you want to diagnosise?
If you want to see all the connected nodes in on line, you can monitor through, Step7--> Select the Project --> Go to PLC --> Select "Display Accessible Nodes". It will be display whatever connected node with address.
Regards,
Appa
Hi Kev,
Is this the same machine you were referring to in this thread by any chance?
Try this, it's a bit of a long shot but you never know:
- Open HW Config
- Press 'CTRL-ALT-F11'
- Save & compile
- Download to PLC
This should force a rebuild of your address container and delete any non-registered addresses.
Kevin H
Sorted!
Thanks Kev. A really quick fix was just what i was after.
No more flashing red lights means happy boss! (even if he did create the problem in the first place as it happens!)
It wasn't the same machine i was asking about in an earlier thread. That turned out to be a mixture of rubbish profibus cable and slowly failing i/o slave module.
Thanks again
Kev
I have an 1769-L16ER that I use to test code and I just found that I can't create MSG tags at the local program scope - they have to be done at...
195
Hi all, This is going to be a long post apologies. I'm also a complete beginner to the world of PLCs. I'm currently working on my first ever...
459
Greetings All, I recently decided to start freelancing in Controls and Automation part time, most of my experience has been with Rockwell...
157
hello, I am using Beckhoff with TwinCAT3 and when I change or add some new hardware or for any reason, there is a mismatch in the real hardware vs...
133
I've ready through the the previous posts, and we've worked with safety design for a long time. In the past, we worked with Pilz directly, and...
588